Smoke Sensor LED issue.

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Smoke Sensor LED issue.
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 11:49 PM . Last Modified: ‎2024-04-05 04:48 AM

0 Likes
4
987
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 11:49 PM . Last Modified: ‎2024-04-05 04:48 AM

Smoke Sensor LED issue.

 I've connected my Smoke sensor to my Sensor Pod on my Netbotz Device however no lights are blinking but the netbotz sees the device. 

 

On Another device I've tested the sensor with smoke, it detected it but now the device alarm alert stays on even when there is clearly no smoke in the area.

(CID:125211405)

Labels
  • Labels:
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 11:49 PM . Last Modified: ‎2024-04-05 04:48 AM

0 Likes
2
987
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 11:49 PM . Last Modified: ‎2024-04-05 04:48 AM

Hi Amit,

 

According to the install guide:

http://www.apc.com/salestools/JSAI-7FGLN8/JSAI-7FGLN8_R1_EN.pdf

The LEDs should blink as follows:

The Smoke Sensor LEDs function as follows: • Both LEDs will blink simultaneously once every ten seconds during the power-up sequence. • The green LED will blink once every five seconds to indicate normal operation. • The red LED will blink once every five seconds to indicate that the Smoke Sensor is out of sensitivity. • The red LED will turn on when the Smoke Sensor reports an alarm state.

It is quite possibly a hardware issue. If the hardware is no operating correctly, replacement can be obtained by calling tech support. a replacement can not be processed through this site. Since you already have one working (you stated there is another in alarm) you can always sty connecting it to the port where this one fails to make sure it is not a power issue.

 

As for the sensor staying in alert even after the smoke is gone, this is by design. It was decided that it may not be prudent to allow the alarm to be cleared as easily as other alarms. A reboot of the device or at least disconnecting and reconnecting the sensor should clear the alarm. 

 

Thanks,

Steve

(CID:125211604)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 11:49 PM . Last Modified: ‎2024-04-05 04:48 AM

In response to DCIM_Support
0 Likes
0
987
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 11:49 PM . Last Modified: ‎2024-04-05 04:48 AM

Hi Amit,

 

Just a note on this. I worked with engineering and we saw that once plugged in, the clear/yellowish LED does appear to flash but it is so faint that it is difficult to see. If you can put the unit in a dark space to verify, you may be able to see it better.


Steve.



(CID:125212388)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 11:49 PM . Last Modified: ‎2024-04-05 04:48 AM

In response to DCIM_Support
0 Likes
0
987
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 11:49 PM . Last Modified: ‎2024-04-05 04:48 AM

NBES0307.MOV

Here's what we saw.

(CID:125212395)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 11:49 PM . Last Modified: ‎2023-10-22 03:57 AM

0 Likes
0
987
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 11:49 PM . Last Modified: ‎2023-10-22 03:57 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of