Server Access console does not open

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Server Access console does not open
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
126
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:22 AM . Last Modified: ‎2024-04-05 03:31 AM

0 Likes
9
1631
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:22 AM . Last Modified: ‎2024-04-05 03:31 AM

Server Access console does not open

Hello Team,

we have a customer with Server Access installed in DCO version 7.5. We are testing to configure the access with IPMI to one UCS server. The server is discovered properly but when we click the button test in the server access remote console menu, nothing happens. I think a browser should open with the IP of the server.

When we test to connect with a browser manually, it works fine. So, it seems that there is not a default browser configured into DCO and it does not know where open the link.

Is there anyway to configure a browser for this in DCO?

Regards

(CID:127534936)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:23 AM . Last Modified: ‎2024-04-05 03:20 AM

0 Likes
3
1631
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:23 AM . Last Modified: ‎2024-04-05 03:20 AM

Javier, thanks for sending log file information.

 

If you logon to your ITO server, and open a browser (like IE, chrome or firefox) you should be able to browse to http://localhost:8688/DataCenterManager and see a console window like the I pasted below.

There should be an entry for each discovered IPMI based device in the view and if you select one you should see details like the below screenshot.

If you look at the details view there is a line called capabilities (highlighted in blue above) which should include words like monitoring, power on/off and so on. Does your entry for the UCS server include those entries?

The tab to the right of the details tab (both highlighted in yellow in the above window) should be an events tab. Are there events listed in that window? The log files you sent suggest there may be a communication issue between the ITO server and the UCS management card... but its not 100% clear in the log file whether those messages are specific to this UCS server ... the events pane will have the messages specific to this device.

Again from the ITO server, the next test is to browse to https://localhost:8643/VirtualGatewayConsole/ from which you should see a console like the one I pasted below.

You should see an entry for your UCS server here too. Select that entry, then in the middle of the window there should be a "Virtual KVM" pane will a "remote access" button ... click that button to test whether the console connection can be made.

Regards

Greg Sterling

(CID:128062335)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:22 AM . Last Modified: ‎2024-04-05 03:20 AM

0 Likes
0
1631
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:22 AM . Last Modified: ‎2024-04-05 03:20 AM

Hello Javier, can you confirm the model of the UCS server and the firmware running  on its management card?

Regards

Greg Sterling

(CID:127534970)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:22 AM . Last Modified: ‎2024-04-05 03:20 AM

0 Likes
0
1631
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:22 AM . Last Modified: ‎2024-04-05 03:20 AM

Hi Greg,

The model is: Cisco UCS B200 M4,but I do not know how to see the firmware on its management card.

This is the information that appears in the External Systems Tab from ITO, Model, Manufacturer are unknown, and IP address is also empty, it should be: 172.26.224.166

Regards

 

(CID:127534998)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:23 AM . Last Modified: ‎2024-04-05 03:20 AM

0 Likes
0
1631
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:23 AM . Last Modified: ‎2024-04-05 03:20 AM

Can you share log files? I attached a zip file which describes the process of collecting a support zip from ITO.

ITO-Collecting-a-Support-Zip.pdf

I'd like to see if an error is being reported.

Greg

(CID:127535521)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:23 AM . Last Modified: ‎2024-04-05 03:20 AM

0 Likes
0
1631
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:23 AM . Last Modified: ‎2024-04-05 03:20 AM

Hello Greg,

I have attached both log files. Could you check it today? Tomorrow we have a meeting with the customer to deliver this project and this issue should be fixed.CustomerSupport.zip2018-01-08--09-34-38.rar

Regards

(CID:128059242)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:23 AM . Last Modified: ‎2024-04-05 03:20 AM

0 Likes
3
1632
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:23 AM . Last Modified: ‎2024-04-05 03:20 AM

Javier, thanks for sending log file information.

 

If you logon to your ITO server, and open a browser (like IE, chrome or firefox) you should be able to browse to http://localhost:8688/DataCenterManager and see a console window like the I pasted below.

There should be an entry for each discovered IPMI based device in the view and if you select one you should see details like the below screenshot.

If you look at the details view there is a line called capabilities (highlighted in blue above) which should include words like monitoring, power on/off and so on. Does your entry for the UCS server include those entries?

The tab to the right of the details tab (both highlighted in yellow in the above window) should be an events tab. Are there events listed in that window? The log files you sent suggest there may be a communication issue between the ITO server and the UCS management card... but its not 100% clear in the log file whether those messages are specific to this UCS server ... the events pane will have the messages specific to this device.

Again from the ITO server, the next test is to browse to https://localhost:8643/VirtualGatewayConsole/ from which you should see a console like the one I pasted below.

You should see an entry for your UCS server here too. Select that entry, then in the middle of the window there should be a "Virtual KVM" pane will a "remote access" button ... click that button to test whether the console connection can be made.

Regards

Greg Sterling

(CID:128062335)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:23 AM . Last Modified: ‎2024-04-05 03:20 AM

In response to DCIM_Support
0 Likes
0
1631
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:23 AM . Last Modified: ‎2024-04-05 03:20 AM

Hi Greg,

I can enter in the first page, I have attached a screenshoot with the information regarding to this UCS. Events' tab is empty:

The view VirtualGatewayConsole does not open, could it be a network problems due to the port :8643? I receive this errror:

Regards

(CID:128062345)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:23 AM . Last Modified: ‎2024-04-05 03:20 AM

In response to DCIM_Support
0 Likes
0
1631
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:23 AM . Last Modified: ‎2024-04-05 03:20 AM

Javier.

Can you collect all of the following log files into a zip file and post it here? This request will include more log info than the customer_support.zip you originally sent.

Please add all the log files from the following log folders to one or more zip files and link them to this posting.

Folder C:\Program Files\Intel\VirtualGateway\logs

Folder C:\Program Files\Intel\DataCenterManager\logs

The log files will help us better understand what's happening.

 

Regarding the connection error in your screenshot. Does your ITO server hostname (V00SIWI-000363) resolve in DNS? If not then the error you're showing is common.

To address this error you will need to edit two files and restart the Intel Virtual KVM and Intel DataCenter Manager services.

  1. Edit the file C:\Program Files\Intel\DataCenterManager\external\apache-tomcat\webapps\VirtualGatewayConsole\settings.xml

    The file will probably look like this:


    https://V00SIWI-000363:8643/DcmMW/WsProxy/Dcm.DcmPort>
    V00SIWI-000363
    8263
    http://V00SIWI-000363:8688/DcmMW/WsEventListener/>
    https://V00SIWI-000363:8643/DcmMW/DcmFiles>
    ./data_files/
    true
    false
    true
    true


    Substitute the IP address of your ITO server for V00SIWI-000363 and save the file.

  2. Edit the file C:\Program Files\Intel\DataCenterManager\external\apache-tomcat\webapps\DataCenterManager\settings.xml

    Change the ITO server hostname to the IP address of the ITO server like in step #1.

  3. From the windows services control panel, restart the Intel Virtual KVM Gateway service (bottom entry highlighted below). Restarting that service should ask you to restart the top service.

 

Now retry connecting to the virtual gateway console.

Regards

Greg Sterling

(CID:128062353)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:23 AM . Last Modified: ‎2024-04-05 03:20 AM

In response to DCIM_Support
0 Likes
0
1631
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:23 AM . Last Modified: ‎2024-04-05 03:20 AM

Hi Greg,

I think the problem has been fixed. We have changed the IP in the config files and now we have access to the VirtualGatewayConsole page, and it says that this equipment does not support remote KVM, so I think with other device the remote console should open.

Thanks for your support.

(CID:128062359)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 03:23 AM . Last Modified: ‎2023-10-22 03:54 AM

0 Likes
0
1631
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 03:23 AM . Last Modified: ‎2023-10-22 03:54 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore