Sensors in DCE and DCO

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Sensors in DCE and DCO
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
125
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 08:42 PM . Last Modified: ‎2024-04-04 04:06 AM

0 Likes
6
1234
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 08:42 PM . Last Modified: ‎2024-04-04 04:06 AM

Sensors in DCE and DCO

 

Hi team,

 

   I have an environmental sensor providing temperature and humidity values in DCE as shown in figure. However once linked with DCE, I have two objects, the environmental monitor and a temperature sensor, but not a humidity sensor. Humidity is not present in DCO. Is it possible to have humidity as well?

 

  Thanks!

(CID:132668263)

Labels
  • Labels:
  • Data Center Expert
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 08:42 PM . Last Modified: ‎2024-04-04 04:05 AM

0 Likes
1
1234
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 08:42 PM . Last Modified: ‎2024-04-04 04:05 AM

Hi

DCO does support humidity sensors, but based on your screen shot it seem like you have associated the device itself and not the actual sensor.

When you find the device in the "Unassociated devices" tab, then you can drag each individual sensor (indicated in blue) on to a rack, but you should only associate the actual device with a device inside the rack, although that will not make any difference regarding temperature and humidity.

 

If your device does not show up with a humidity sensor, then my guess would be that DCE reports that humidity sensor in a way which DCO does not recognize - a situation which sometimes can be remedied by updating the DDF for that device.

Best,

Gert

(CID:132669267)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 08:42 PM . Last Modified: ‎2024-04-04 04:05 AM

0 Likes
0
1234
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 08:42 PM . Last Modified: ‎2024-04-04 04:05 AM

I'm very interested in this... as we are about to integrate a LOT of these via RFCode Centerscape. 

(CID:132668319)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 08:42 PM . Last Modified: ‎2024-04-04 04:05 AM

0 Likes
1
1235
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 08:42 PM . Last Modified: ‎2024-04-04 04:05 AM

Hi

DCO does support humidity sensors, but based on your screen shot it seem like you have associated the device itself and not the actual sensor.

When you find the device in the "Unassociated devices" tab, then you can drag each individual sensor (indicated in blue) on to a rack, but you should only associate the actual device with a device inside the rack, although that will not make any difference regarding temperature and humidity.

 

If your device does not show up with a humidity sensor, then my guess would be that DCE reports that humidity sensor in a way which DCO does not recognize - a situation which sometimes can be remedied by updating the DDF for that device.

Best,

Gert

(CID:132669267)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 08:42 PM . Last Modified: ‎2024-04-04 04:05 AM

In response to DCIM_Support
0 Likes
0
1234
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 08:42 PM . Last Modified: ‎2024-04-04 04:05 AM

I have asked for the modified DDF, but no news for the moment.

Fingers crossed!

(CID:133367462)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 08:42 PM . Last Modified: ‎2024-04-04 04:05 AM

0 Likes
0
1234
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 08:42 PM . Last Modified: ‎2024-04-04 04:05 AM

Wes, you might find this helpful:

RF Code CenterScape Connector

(CID:132669270)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 08:42 PM . Last Modified: ‎2024-04-04 04:05 AM

0 Likes
0
1235
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 08:42 PM . Last Modified: ‎2024-04-04 04:05 AM

Thanks for your answer, 

 

    humidity sensor is not present in DCO, so I assume the DDF is not working well.

 

    I will try to update it and let you know.

 

   Regards

(CID:132669282)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 08:42 PM . Last Modified: ‎2023-10-22 03:53 AM

0 Likes
0
1235
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 08:42 PM . Last Modified: ‎2023-10-22 03:53 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore