Relation between NetBotz 450 and DCE

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Relation between NetBotz 450 and DCE
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
64
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:08 PM . Last Modified: ‎2024-04-08 12:44 AM

0 Likes
11
1646
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:08 PM . Last Modified: ‎2024-04-08 12:44 AM

Relation between NetBotz 450 and DCE

If i have in many sites one NB450 than is collect info from temperature, humidity sensor and SNMP SAI, every NB450 are connected to a DCE (ver. 7.4.2) but alerts are send by NB450 nor from DCE. Is there, any way to make email send of alarm by DCE, may a firmware, ddf.. ?

(CID:118622757)

Labels
  • Labels:
  • Data Center Expert
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:09 PM . Last Modified: ‎2024-04-08 12:44 AM

0 Likes
6
1646
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:09 PM . Last Modified: ‎2024-04-08 12:44 AM

Hi Miguel,

 

NetBotz have always sent their own alerts. This has been the case since NetBotz Central. This is still the case. There is no way to make DCE send alerts for NetBotz without re-coding the system. NetBotz are not SNMP or Modbus devices. It is an HTTP communications that sends across XML information and does not use a DDF. 

 

Thanks,

Steve.

(CID:118622793)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 11
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:09 PM . Last Modified: ‎2024-04-08 12:44 AM

0 Likes
6
1647
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:09 PM . Last Modified: ‎2024-04-08 12:44 AM

Hi Miguel,

 

NetBotz have always sent their own alerts. This has been the case since NetBotz Central. This is still the case. There is no way to make DCE send alerts for NetBotz without re-coding the system. NetBotz are not SNMP or Modbus devices. It is an HTTP communications that sends across XML information and does not use a DDF. 

 

Thanks,

Steve.

(CID:118622793)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:09 PM . Last Modified: ‎2024-04-08 12:44 AM

In response to DCIM_Support
0 Likes
0
1646
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:09 PM . Last Modified: ‎2024-04-08 12:44 AM

If DCE can detect the lost of communication of NB, How can do for send DCE a SMS o email with this alert. Becuase if i lost the communication NB can't send this alarm

(CID:119049836)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:09 PM . Last Modified: ‎2024-04-08 12:44 AM

In response to DCIM_Support
0 Likes
0
1646
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:09 PM . Last Modified: ‎2024-04-08 12:44 AM

Hi Miguel,

Lost comm is different. It is not the same as a breached humidity threshold on the bot. If you have any users on DCE that have rights to view that bot AND their e-mail is configured with their user (either local or in Active Directory), they should receive a lost comm message when DCE can no longer communicate with the bot.

 

 Additionally, just because DCE loses comm with a device does not mean the device itself is unable to alert. It is always possible that there is a network outage between the 2 systems.

 

Steve

(CID:119049839)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:09 PM . Last Modified: ‎2024-04-08 12:43 AM

In response to DCIM_Support
0 Likes
0
1646
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:09 PM . Last Modified: ‎2024-04-08 12:43 AM

Steve, But how can add this alert to the policy notify than have the emails relation that have to recive this alarm?

(CID:119049845)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:09 PM . Last Modified: ‎2024-04-08 12:43 AM

In response to DCIM_Support
0 Likes
0
1646
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:09 PM . Last Modified: ‎2024-04-08 12:43 AM

Miguel,

 

There is no policy. If you have a user and If that user has rights to this NetBotz and If he has an e-mail associated when you create the user, he will get an e-mail. No policy necessary.

IN the case shown where Steve is an admin and his user has an e-mail configured, steve@apc.com will get an e-mail if any NetBotz goes off-line. If not an admin, he has to have specific rights to the group/folder where the NetBotz resides.

 

Steve

 

(CID:119049854)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:09 PM . Last Modified: ‎2024-04-08 12:43 AM

In response to DCIM_Support
0 Likes
0
1646
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:09 PM . Last Modified: ‎2024-04-08 12:43 AM

ok, But this mail can´t be configurable?

(CID:119050672)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:09 PM . Last Modified: ‎2024-04-08 12:43 AM

In response to DCIM_Support
0 Likes
0
1646
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:09 PM . Last Modified: ‎2024-04-08 12:43 AM

That is correct. IF the user has an e-mail and if they have access to the bot, they should receive an e-mail. There has been an enhancement request in to make this more configurable but as of yet, nothing has been added.

(CID:119050674)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:09 PM . Last Modified: ‎2024-04-08 12:43 AM

0 Likes
2
1646
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:09 PM . Last Modified: ‎2024-04-08 12:43 AM

Hi Miguel angel solans,

Four years ago I had a similar task. And I successfully solved it as follows (unless of course you do not have many hundreds of NetBotz appliances).

First, all NetBotz appliances must be discovered on the target DCE-server. Since it is impossible for sensors from NetBotz appliances to create Alarm Thresholds in the DCE-server, for each such sensor I created a Virtual Sensor in the DCE-server. Further for each virtual sensor I was able to easily create Alarm Thresholds and configure them accordingly. After checking the functioning of virtual sensors and alarm thresholds, I completely turned off alarm thresholds on all NetBotz appliances. And now all alarms are sent only by one DCE-server, and not by a bunch of NetBotz appliances 😀.

And this solution has been working for a year now.

With respect.

(CID:118623048)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:09 PM . Last Modified: ‎2024-04-08 12:43 AM

In response to DCIM_Support
0 Likes
0
1646
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:09 PM . Last Modified: ‎2024-04-08 12:43 AM

Great. But with state sensor can´t use virtual sensor

(CID:118623052)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:10 PM . Last Modified: ‎2024-04-08 12:43 AM

In response to DCIM_Support
0 Likes
0
1646
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:10 PM . Last Modified: ‎2024-04-08 12:43 AM

Yes it is, and this lack of my decision. But in practice I did not need this.

(CID:118623058)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:10 PM . Last Modified: ‎2023-10-22 03:45 AM

0 Likes
0
1646
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:10 PM . Last Modified: ‎2023-10-22 03:45 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of