Rack mount per outlet metered PDU socket inventory in DCO

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Rack mount per outlet metered PDU socket inventory in DCO
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
109
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
62
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 06:45 PM . Last Modified: ‎2024-04-04 11:26 PM

0 Likes
7
1161
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 06:45 PM . Last Modified: ‎2024-04-04 11:26 PM

Rack mount per outlet metered PDU socket inventory in DCO

I have couple of rack mount per outlet metered PDU in my environment.

Is there any custom solution how I can create an inventory about which device is connected to which PDU socket?

I think it is not just interesting for outlet metered PDU. On a standard basic

APC PDU the outlets are numbered and it would worth to know which outlet is allocated to which device.

(CID:132651187)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 7
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 06:45 PM . Last Modified: ‎2024-04-04 11:26 PM

0 Likes
4
1161
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 06:45 PM . Last Modified: ‎2024-04-04 11:26 PM

Hi Mate,

Currently that's not supported, I can capture a feature request for you? Might not be so practical, but perhaps using custom properties could help a little.

Kind regards

(CID:132651245)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 06:45 PM . Last Modified: ‎2024-04-04 11:26 PM

In response to DCIM_Support
0 Likes
0
1161
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 06:45 PM . Last Modified: ‎2024-04-04 11:26 PM

Work around then,manual mapping using custom properties per what Jef said:create 2 custom properties template

1.for rack pdu outlet at rack pdu itself,to track which outlet is being used,or to which server.

 

2.On the individual server,to track the outlet number of the rack pdu.

 

Its manual and prone to entry error,still better than not tracking.

 

I would suggest to name the rack pdu outlet on the rpdu nmc itself,especially if this is switched outlet rpdu, to avoid switching the wrong outlet....

(CID:132651330)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 06:45 PM . Last Modified: ‎2024-04-04 11:26 PM

In response to DCIM_Support
0 Likes
0
1161
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 06:45 PM . Last Modified: ‎2024-04-04 11:26 PM

Thank you both. I think create a future request would worth as I can see the upvotes not just me interested.

I also thought on custom properties but on PDU side it will be huge amount. For example on a PDU where I have 36 outlets I have to create:

  • outlet1
  • outlet2
  • ...
  • outlet36

Which means 36 custom properties only for a PDU?

(CID:132651349)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 06:45 PM . Last Modified: ‎2024-04-04 11:26 PM

In response to DCIM_Support
0 Likes
0
1161
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 06:45 PM . Last Modified: ‎2024-04-04 11:26 PM

Hi Mate,

I have now registered this as a feature request for you - will send you a direct confirmation as well, thanks.

Kind regards

(CID:132651367)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 06:45 PM . Last Modified: ‎2024-04-04 11:26 PM

In response to DCIM_Support
0 Likes
0
1161
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 06:45 PM . Last Modified: ‎2024-04-04 11:26 PM

On custom property of rack pdu itself,yes unfortunately 

 

Only one cp per server,set the cp template as a list of fixed number,so user can then just select when setting on server.

 

For rack pdu cp,yes per you said,each cp is for the outlet,to list which server it is connected,or at leat to tell if outlet is in use/available.

 

p.s did raise similar request previously, for the same reason as you....

(CID:132651378)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 06:45 PM . Last Modified: ‎2024-04-04 11:26 PM

0 Likes
0
1160
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 06:45 PM . Last Modified: ‎2024-04-04 11:26 PM

Hi Mate

As others have suggested, if you do decide to try something, I recommend A) focusing on keeping the device to port mapping in one place only and B) ensuring it can be kept up to date.  There's no point starting if you can't pretty much guarantee B.  AFAIK there is no automated way to do either so there is risk involved - this only means that your reward must be sufficient to take the risk.

I would keep the detail on the rPDU (agree with Christopherus' comments above) but I would automate the writing to DCO.  You could use web service calls to read rPDU names from DCE (assuming its included), SNMP to get port/server info from each rPDU and web service calls to write the rPDU name and outlet number to a custom property on the DCO device.

For giggles, it might work something like this.....

  • user (thats you) maintains a text list of all the rPDU model types that are switched
    • could work with APC as well as 3rd party switched  rPDUs!
    • could maintain a list of the rPDU names but I reckon easier this way
  • user ensures the rPDU SNMP / DNS names are unique and matches the name in DCO
    • should be standard practice
  • user ensures the unique DNS names of the connected servers (short or FQDN) are unique and set
    • again should be standard practice.

 

  • The process (to read DCE and write DCO) runs as often as required via cron on DCO server 
    • Gets the list of all rPDU names by model name from DCE
    • Knows the SNMP objects (OIDs) that hold the server names
      • I don't believe DCE holds the info? so have to read from rPDU
    • Reads the port number / server name list
    • Writes the rPDU name and port number to the device in DCO
      • perhaps checking the device is in the same rack as the rPDU?
      • perhaps alerting for server names set on the rPDU which aren't in DCO?
      • perhaps alerting for DCO servers in racks with switched rPDUs that aren't set on rPDU?
    • Logs activity / send email summary 

Just thinking out loud.  Let me know if you'd like to have a go.

Cheers

Ed

 

 

(CID:132651605)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 06:45 PM . Last Modified: ‎2023-10-22 03:43 AM

0 Likes
0
1160
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 06:45 PM . Last Modified: ‎2023-10-22 03:43 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of