Posted: 2020-07-02 05:11 PM . Last Modified: 2024-04-09 02:33 AM
Hi, I would like to make power supply model in small server room with distributed redundant "catcher" UPS configuration as this way as in the picture below:
I have problem because the "catcher" show, that "Reserved capacity" ist twice as bigger then UPS (see below).
For example load on STS is
What am I doing wrong? (I use DCO version 7.5).
I will be grateful for the help,
Zenon
(CID:104173558)
I change my model as this way as in the picture below:
and "Reserved capacity" of the BYPASS-UP is the same as the UPS.
Thanks for the help.
Best regards,
Zenon
(CID:104173692)
Hi Zenon
Unfortunately the capacity calculations in Operation 7.5 does not handle the situation above very well. I have a suggestion for a work-around which I hope can help.
Work-around:
If you only model one STS instead of the two shown (I know this is different from your physical setup), and then add a PDU to distribute to the two PDUs RS-1 and RS-2, the load on the catcher UPS (BYPASS-UPS) will be correct.
I am also very curious about the setup you have shown, because with the given equipment I would have thought a 2N setup was preferred. Can you help me understand what the benefits of the shown setup are over a traditional 2N setup?
Best,
Niels
(CID:104173655)
Thanks for the help. I will change my model and I will let you know. I must explain, that only I am learning the use DCO now and in my model I used BYPASS-UPS, but it is physical bypass of our UPS powered from the outside grid. Best regards, Zenon
(CID:104173666)
Best regards,
Zenon
(CID:104173692)
Posted: 2020-07-02 05:11 PM . Last Modified: 2023-10-31 11:31 PM