Hi,
I have a problem with connecting Schneider Powerlogic PM 5320 to DCE7.5.
PM5320 has new FW 2.11 and HW is B1.
The DCE recognises the unit trough TCP Modbus protocol but it immediately loses connection and communication error comes up.
The DDF files were downloaded and uploaded.
Also I tryed connecting to Schneider COM X510 but the result is the same.
Am I missing something?
(CID:141269251)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 06:33 PM . Last Modified: 2024-04-03 02:57 AM
Hi Boris Lukinic,
Thanks for posting, and sorry to leave you hanging. Did you resolve your issue or is there still a problem connecting?
Thanks,
Stine
(CID:143754867)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 06:33 PM . Last Modified: 2024-04-03 02:57 AM
It was a problem with the booting of the Powerlogic and COM X510, it requires a special procedure of turning it on and conecting it to network.
The local Schneider office helped.
regards
(CID:143754886)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 06:33 PM . Last Modified: 2024-04-03 02:57 AM
Thanks for sharing! Glad to hear it's resolved.
Cheers,
Stine
(CID:143754888)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 06:33 PM . Last Modified: 2023-10-22 03:37 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.