Power Usage Report Issue - DCE

EcoStruxure IT Forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT Forum
  • Power Usage Report Issue - DCE
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
129
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
72
View All

Recommended Forums

  • APC UPS Data Center & Enterprise Solutions Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT Forum
Start a Topic
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:20 PM . Last Modified: ‎2024-04-08 01:59 AM

0 Likes
5
1469
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:20 PM . Last Modified: ‎2024-04-08 01:59 AM

Power Usage Report Issue - DCE

Hi,

 

I am trying to run a report from DCE to show how much power the data center has been using over a set period. I have created on for a month and set it to 30 minute intervals. The Data which has been produced is massively high.

First report is done in kWh - This screenshot is for 1 PDU, I have a total of 46 PDUs.

I have a virtual sensor which shows the data center running at 868,827.7 kWh.

I have a second sensor which shows the usage in amps. 166.3A

This data seems massively incorrect, can someone explain to me what is happening and why I am seeing such high results?

 

I have to run this report for 2 data centers, one for a 12 month period, and one for 5 months.

 

(CID:110792814)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:20 PM . Last Modified: ‎2024-04-08 01:58 AM

0 Likes
3
1469
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:20 PM . Last Modified: ‎2024-04-08 01:58 AM

Hi Martin,

 

Kwh or kilowatt hours is already a value for power over time. That value on the PDU will continually increase over time. Your actual output at any specific time could actually be 0 watts but the kwh reading could still be high. Here's an example:

 

One issue that I do see with this value coming from the PDU is that it does not show the date it was reset. If you actually look at the PDU using SNMP (I have a modular PDU to look at for this), you can see the kwh "reset" date. The value you're reading for kwh is what the PDU has used since that time:

 

If you are looking for a value to match up with amperage, watts would be the value you're looking for. 

 

Thanks,

Steve

(CID:110792853)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 5
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:20 PM . Last Modified: ‎2024-04-08 01:58 AM

0 Likes
3
1470
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:20 PM . Last Modified: ‎2024-04-08 01:58 AM

Hi Martin,

 

Kwh or kilowatt hours is already a value for power over time. That value on the PDU will continually increase over time. Your actual output at any specific time could actually be 0 watts but the kwh reading could still be high. Here's an example:

 

One issue that I do see with this value coming from the PDU is that it does not show the date it was reset. If you actually look at the PDU using SNMP (I have a modular PDU to look at for this), you can see the kwh "reset" date. The value you're reading for kwh is what the PDU has used since that time:

 

If you are looking for a value to match up with amperage, watts would be the value you're looking for. 

 

Thanks,

Steve

(CID:110792853)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:20 PM . Last Modified: ‎2024-04-08 01:58 AM

In response to DCIM_Support
0 Likes
0
1469
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:20 PM . Last Modified: ‎2024-04-08 01:58 AM

Good explanation Steve.  Think of the kwh like a year to date figure.  If there is a requirement for usage, they just take the reading at the opening date and deduct the reading from the close date.

(CID:110793112)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:20 PM . Last Modified: ‎2024-04-08 01:58 AM

In response to DCIM_Support
0 Likes
0
1469
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:20 PM . Last Modified: ‎2024-04-08 01:58 AM

To leverage on this, for energy (kWh)consumption report, use summary report.

DCE summary report provides both Min and Max for the report period (e.g monthly), which you can then deduct to have the energy consumption of that month.

(CID:110793695)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:20 PM . Last Modified: ‎2024-04-08 01:58 AM

In response to DCIM_Support
0 Likes
0
1469
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:20 PM . Last Modified: ‎2024-04-08 01:58 AM

So to confirm some understanding, when you run the Summary kWh report, you would take the delta value column and total that up to get your total consumption and in the case of the attached screenshot that would be consumption for the day??

(CID:111939390)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:20 PM . Last Modified: ‎2023-10-22 03:36 AM

0 Likes
0
1469
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:20 PM . Last Modified: ‎2023-10-22 03:36 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore