Power Tooltips in Distributed Redundant setups

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Power Tooltips in Distributed Redundant setups
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
109
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
62
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:22 PM . Last Modified: ‎2024-04-09 01:59 AM

0 Likes
11
1367
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:22 PM . Last Modified: ‎2024-04-09 01:59 AM

Power Tooltips in Distributed Redundant setups

Hi Support,

 

It appears there may be an issue with display of Power Tooltips in distributed redundant setups.

 

Here, (screenshot 1) I have a UPS setup as Distributed Redundant feed. This feeds a power panel, and the power panel has 2x breaker panels (configured each for the rack "A" and "B" feeds). 

These feed 2x rack PDUs per rack, one connected to each "A" and "B" feed. The rack PDUs are rated to 32A at 220V.

 

The racks are all in a Capacity group configured as Distribution Redundancy (screenshot 2).

The peak and average loads are exactly as expected for Distribution Redundancy, but you can see in screenshot 1 that the tooltip has disappeared in the Power overlay.

 

In screenshot 3, setting the Advanced Power tooltip in the client preferences correctly shows the rack load against average and peak, but in screenshot 4 you can see that setting the Advanced Power Tooltip in a 2N environment shows only phase information, no failover or measured load.

 

Asset Provisioning advisor and UPS reservation figures are as expected, and powertooltips exist at the UPS and power panel - just not at the rack level.

 

Is there an error in this configuration? 

Even though there is one source feed, I would still have expected to see a power capacity bar chart indicating estimated, failover and measured load for the rack level.

Especially as you can continue to manually add equipment to a rack (and exceed the average and peak values) with no visual indication that there is a problem in the layout / tooltip

 

Thanks,

 

David

 

(CID:105457169)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:22 PM . Last Modified: ‎2024-04-09 01:59 AM

0 Likes
4
1368
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:22 PM . Last Modified: ‎2024-04-09 01:59 AM

Distributed Redundant UPS (DRU), and Distribution Redundancy (DN) are two very different setups and are normally not used together, because DRU requires at least 3 UPS's, but DN is only one UPS where the redundancy lies in the power distribution from the UPS.

If it is DN you want, I would suggest the following steps to get you going:

  • Delete the current capacity group.
  • Change the UPS power feed to A-Feed (which is the same as single as long you do not have B-Feed UPS)
  • Generate the capacity group (CG) with the utility that generates group(s) for an entire room.
  • The CG now has a single UPS feed and and check mark at Distribution Redundancy.

Now the normal tool tip should work.

Although it might not do what you expect because the DN feature was designed with redundant rack PDUs in mind, and it does not recognize breaker panels as being redundant  - it does however work (to some extend) for redundant Power Panels/PDUs.

The advanced tool tip are an fairly old feature and they might be missing some of the information you get in the normal tool-tip.

For more information of DRU setups I would recommend you to look at APC White Paper 75, especially figure 4, 5 and 6.

If you do create a DRU setup please always use the utility that generates group(s) (CG) for an entire room, because manual creating CGs to a rack will not pick up the DRU setup and the CG will not be configured correctly leading to issues like nonfunctional tool-tips.

Kind Regards

Gert

(CID:105457204)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 11
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:22 PM . Last Modified: ‎2024-04-09 01:59 AM

0 Likes
0
1368
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:22 PM . Last Modified: ‎2024-04-09 01:59 AM

Hi David, I have sent you an invite to my =S= box, just in case if you would kindly share a copy of your solution with me, then I will take a look, thanks. Kind regards

(CID:105457187)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:22 PM . Last Modified: ‎2024-04-09 01:59 AM

0 Likes
0
1368
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:22 PM . Last Modified: ‎2024-04-09 01:59 AM

Hello David, Based on the screen shoots provided it would appear that all racks are being feed by the same UPS and the same phase on that UPS. Being that the rack is being feed by one UPS the model will not display any failover load because IT Load will not failover to another UPS. To be able to determine this exactly we would require a backup of your configuration to confirm my speculations. Thanks Victor

(CID:105457194)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:22 PM . Last Modified: ‎2024-04-09 01:59 AM

0 Likes
4
1369
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:22 PM . Last Modified: ‎2024-04-09 01:59 AM

Distributed Redundant UPS (DRU), and Distribution Redundancy (DN) are two very different setups and are normally not used together, because DRU requires at least 3 UPS's, but DN is only one UPS where the redundancy lies in the power distribution from the UPS.

If it is DN you want, I would suggest the following steps to get you going:

  • Delete the current capacity group.
  • Change the UPS power feed to A-Feed (which is the same as single as long you do not have B-Feed UPS)
  • Generate the capacity group (CG) with the utility that generates group(s) for an entire room.
  • The CG now has a single UPS feed and and check mark at Distribution Redundancy.

Now the normal tool tip should work.

Although it might not do what you expect because the DN feature was designed with redundant rack PDUs in mind, and it does not recognize breaker panels as being redundant  - it does however work (to some extend) for redundant Power Panels/PDUs.

The advanced tool tip are an fairly old feature and they might be missing some of the information you get in the normal tool-tip.

For more information of DRU setups I would recommend you to look at APC White Paper 75, especially figure 4, 5 and 6.

If you do create a DRU setup please always use the utility that generates group(s) (CG) for an entire room, because manual creating CGs to a rack will not pick up the DRU setup and the CG will not be configured correctly leading to issues like nonfunctional tool-tips.

Kind Regards

Gert

(CID:105457204)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:22 PM . Last Modified: ‎2024-04-09 01:59 AM

In response to DCIM_Support
0 Likes
0
1368
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:22 PM . Last Modified: ‎2024-04-09 01:59 AM

Hi Gert, Thanks for your reply - that is exactly the answer I'm looking for and has resolved the issue David

(CID:105457222)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:22 PM . Last Modified: ‎2024-04-09 01:59 AM

In response to DCIM_Support
0 Likes
0
1368
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:22 PM . Last Modified: ‎2024-04-09 01:59 AM

Hi Gert / All, Is there anywhere else I can get a copy of WP-75? The link to this appears to be broken on the website... Thanks, David

(CID:105457775)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:22 PM . Last Modified: ‎2024-04-09 01:59 AM

In response to DCIM_Support
0 Likes
0
1368
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:22 PM . Last Modified: ‎2024-04-09 01:59 AM

I usually just use google and search for "apc whitepaper 75" you could try this link: http://www.apcmedia.com/salestools/SADE-5TPL8X/SADE-5TPL8X_R3_EN.pdf?sdirect=true

(CID:105457783)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:22 PM . Last Modified: ‎2024-04-09 01:59 AM

In response to DCIM_Support
0 Likes
0
1368
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:22 PM . Last Modified: ‎2024-04-09 01:59 AM

Thanks Gert - that link works

(CID:105457790)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:23 PM . Last Modified: ‎2024-04-09 01:59 AM

0 Likes
0
1368
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:23 PM . Last Modified: ‎2024-04-09 01:59 AM

Hi Victor / Jef, Thanks for the reply. The setup above is a test setup after a customer question, but yes, there is one UPS and the redundancy is in the distribution level (so a rack A and B feed originates from that one UPS). At 32A, 220V a rack peak load capacity would be: 32 x 220 x 0.8 = 5632W If there are 2 rack PDUs, it would be 11KW (assuming no distribution redundancy). If distribution redundancy is required, then rack peak load capacity would be reduced to 5.6kW. If the Capacity Group in this scenario is configured with Distribution Redundancy in DCO, it correctly reflects the same number of 5.6kW. Thinking about it, 'failover' is probably the wrong term to use here as there is no second UPS to fail over to, only a second rack PDU. And again, 'failover' is still not correct as one PDU could be 80% loaded and one 20% - and Distribution Redundancy would still be maintained. I guess the answer in this case, would be that the tooltip should probably display a bargraph of maximum available capacity 5.6kW, turning red in the overlay if overloaded. If the Capacity Group is removed in DCO, the bargraph is actually restored but showing the non-resilient 11kW as available capacity. It's not a problem if Asset Provisioning is used, but the problem is really that with the Capacity Group set to Distribution Redundancy (5.6kW), I can manually load that rack beyond it's resilience level and there is no visual indication in DCO other than a recommendation once the rack is already overloaded. If the rack is left out the Capacity Group, it turns red on overload and shows a tooltip with the load figures. I have attached a file with screenshot with a rack overloaded to 12kW, both when it's in and out of a Capacity Group. Hope this makes sense?

(CID:105457207)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:23 PM . Last Modified: ‎2024-04-09 01:59 AM

0 Likes
0
1368
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:23 PM . Last Modified: ‎2024-04-09 01:59 AM

When in a capacity group:

5.jpg

(CID:105457209)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:23 PM . Last Modified: ‎2024-04-09 01:59 AM

0 Likes
0
1368
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:23 PM . Last Modified: ‎2024-04-09 01:59 AM

When not in a capacity group:

6.jpg

(CID:105457211)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:23 PM . Last Modified: ‎2023-10-31 11:30 PM

0 Likes
0
1368
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:23 PM . Last Modified: ‎2023-10-31 11:30 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of