Power Tool Tip - UPS - Potential Failover Load (Exceeds Reserved Load)
  • EcoStruxure IT forum
  • Power Tool Tip - UPS - Potential Failover Load (Exceeds Reserved Load)
124
110
65
Back to EcoStruxure IT forum
Posted: ‎2020-07-02 05:40 PM . Last Modified: ‎2024-04-09 02:14 AM
620
DCO CoLo 7.5
Could some please explain or point to the doco for this UPS tool tip.  In the example below for a 160kW UPS, somewhere 47kW is being reserved.  There are no capacity groups and no Reserved power per rack set (yet).  As a test I set the reserved power to per rack to 5.9kW but same issue
http://dcimsupport.apc.com/display/public/UAOp74/Power+Tool+Tip+Troubleshooting
With "Advanced Power" Tool Tip on or off, the display is the same
(CID:104174663)
  • Data Center Operation
Replies 4
619
Hi Ed,
Here is the documentation regarding our tool tips.
What does the power tool tip tell me
Jesper
(CID:104174687)
Thanks Jesper,
On further consideration, am I correct in saying that in this case, both the Reserved Load and Estimated Load failed over are the same thing so the error about "Potential fail-over load exceeds reserved load" is probably as a result of a rounding error?  If that is the case, could you submit as a bug fix / feature request?  If not, what is the red alert trying to tell me?
(CID:104174845)
Hi Ed, Potential fail-over load is the load we reserver in case another UPS fails. So if you have a setup a A and B-feed setup will we show the power needed on the A UPS in case the B UPS fails. The estimated load is the total estimated load of the equipment in the group.
(CID:104174846)
Posted: ‎2020-07-02 05:40 PM . Last Modified: ‎2023-10-31 11:30 PM