We have the following power path on DCO for our customer’s installation:
Generic 3P Power Panel => 16A 1P Circuit Breakers (2x, on phases L1 and L2 respectively) => Left & Right 16A PDUs => IT equipment
We are facing the following issue when trying to select power dependency on any of the rack IT equipment: “Please set correct voltages on rack PDU to enable phase selection.” (see screenshot below).
I am also attaching screenshots of the settings of the various equipment of the power path.
Could someone explain how I can solve the above issue?
(CID:148771616)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 10:16 PM . Last Modified: 2024-04-03 12:31 AM
HI!
Did you check Power Panel output voltage? It's 208V by default if I'm not mistaken.
You should set it to 400V.
(CID:148771881)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 10:16 PM . Last Modified: 2023-10-22 03:33 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.