I did the configuration and associated the script with the DCE sensors the reading is accurate on the devices but while i'm evaluating the PUE it is showing no data. Jef can u pls help me ?
(CID:117999577)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 03:41 PM . Last Modified: 2024-04-08 12:53 AM
Hi Waseem,
Currently when PUE showing "No data", that means the energy efficiency calculations have been unsuccessful (usually due to misconfiguration). That's great you already have verified scripts to see if they can be evaluated, however there might be other settings/configurations that might be "incorrect". As suggested in the following tip: , it would be good idea to start out small and just associate a few devices at a time and evaluate the system often...
You might also want to watch this video tutorial illustrating nicely an EE setup How to measure the data center energy efficiency
PS. it seems you might be running 8.0, so I would like to recommend upgrading to the latest version (currently 8.1), that contains many enhancements (including the way UI/client should display the script folder(s) only once on screen and not being displayed multiple times).
Kind regards
(CID:117999845)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 03:41 PM . Last Modified: 2024-04-08 12:53 AM
This is the script evaluate similarly for all it is accurate but still in when i calculate pue it shows no data.
(CID:117999599)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 03:41 PM . Last Modified: 2024-04-08 12:53 AM
Hi Waseem Khan,
thanks for posting. Lets see who can be of assistance here. @community any ideas?
Kind regards Ditte
(CID:117999656)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 03:41 PM . Last Modified: 2024-04-08 12:53 AM
Hi Waseem,
Currently when PUE showing "No data", that means the energy efficiency calculations have been unsuccessful (usually due to misconfiguration). That's great you already have verified scripts to see if they can be evaluated, however there might be other settings/configurations that might be "incorrect". As suggested in the following tip: , it would be good idea to start out small and just associate a few devices at a time and evaluate the system often...
You might also want to watch this video tutorial illustrating nicely an EE setup How to measure the data center energy efficiency
PS. it seems you might be running 8.0, so I would like to recommend upgrading to the latest version (currently 8.1), that contains many enhancements (including the way UI/client should display the script folder(s) only once on screen and not being displayed multiple times).
Kind regards
(CID:117999845)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 03:41 PM . Last Modified: 2024-04-08 12:53 AM
Thank-you Jef Faridi i will try connecting few equipment's only to test.
i have a question is it necessary to define power path in same data center to calculate PUE because in this case i have not defined the power path i have just created a simple electrical room in which i have placed all the equipment's without connecting them and associated with dce virtual sensors.
Pls suggest ?
(CID:117999872)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 03:41 PM . Last Modified: 2024-04-08 12:52 AM
Hi Wassem,
It is not necessary to define power path for rack pdu's etc in the data center, but there should be power path between the switchgear and UPS/PDU.
Kind regards
(CID:117999988)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 03:42 PM . Last Modified: 2024-04-08 12:52 AM
Thank-you Jef Faridi the issue has been solved.
Pue up and running.
(CID:118000233)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 03:42 PM . Last Modified: 2024-04-08 12:52 AM
Hi Wassem,
Excellent, many thanks for the update, appreciated.
Kind regards
(CID:118000240)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-03 03:42 PM . Last Modified: 2023-10-22 03:32 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.