Are NetBotz Sensors, T, H & TH, monitor sensors capable to monitor Outdoor environment- eg, Outdoors of a Prefab.
Do they need to be placed in a IP rated shelters / cabinets / protected etc.
What is the environmental impact on the sensors- eg. from Rain, Snow, dust extreme heat & wind? Are there any IP ratings involved? Or Any specific IP rated NB sensors are orderable?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-01-03 07:45 AM
Hi @sesa241642 ,
NetBotz and it's associated sensors are designed for indoor use only. They are designed for use in an IT environment.
If you look at the following sensor for instance:
https://www.apc.com/shop/us/en/products/APC-Temperature-Humidity-Sensor/P-AP9335TH
You can see: