Netbotz v3 alarms displayed in DCE - what is the expected delay

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Netbotz v3 alarms displayed in DCE - what is the expected delay
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: โ€Ž2020-07-02 12:55 PM . Last Modified: โ€Ž2024-04-09 11:40 PM

0 Likes
5
733
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-02 12:55 PM . Last Modified: โ€Ž2024-04-09 11:40 PM

Netbotz v3 alarms displayed in DCE - what is the expected delay

Hi guys,

I would like to confirm if Netbotz alarms (3xx,4xx,5xx series) will appear in DCE instantly or will there be a default delay I should expect.

I have done some tests with DCE monitoring Netbotz 570.
Netbotz has couple of NBPD0170s on an A-Link.
When door open alarm is picked up by Netbotz this alarm will not appear in DCE until the next DCE poll (confirmed multiple times via tests).

I have been reading manuals and also came across this link Post Alert Data Settings option that makes me believe Netbotz alerts should appear in DCE almost instantly if Post Alert settings are done correctly.
I need to go back and verify if my Netbotz has this configured correctly (I did not change it and I relied on automatic configuration during discovery process). 

Can you please confirm if Netbotz alarms will appear almost instantly in DCE? or will it be on the next DCE poll?

(CID:97484825)

Labels
  • Labels:
  • Data Center Expert
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: โ€Ž2020-07-02 12:55 PM . Last Modified: โ€Ž2024-04-09 11:40 PM

0 Likes
1
733
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-02 12:55 PM . Last Modified: โ€Ž2024-04-09 11:40 PM

Hi Marcis,

 

The NetBotz appliance should post to DCE almost immediately. If it is not, take a look at the "Data Center Expert" applet in Advanced View. Is this set to post to DCE using IP or name? If it is set to name, there could be a DNS issue. Make sure the appliance can ping the DCE server by name. If it can not, even with the correct DNS, delete the entry with the name. 

 

Next, go to device, NetBotz appliance configuration, post alert data settings. Where it says "Select the Address to Use for Sending Alert Data", select the IP of the server instead of the name and click OK. This should recreate the entry in the NetBotz appliance by IP.

 

If the appliance was already posting to IP, check the logs on the bot. Create an alert and immediately afterwards, go to the unit's web page and look at http:///pages/support.html

Here, you can do things like ping and you can also hit logread to read the events. Are you getting any errors posting to the DCE server? If there is a router / firewall between the DCE and NetBotz appliance, your posts could be blocked. 

 

Steve

(CID:97484876)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Replies 5
DCIM_Support
Picard DCIM_Support
Picard

Posted: โ€Ž2020-07-02 12:55 PM . Last Modified: โ€Ž2024-04-09 11:40 PM

0 Likes
1
733
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-02 12:55 PM . Last Modified: โ€Ž2024-04-09 11:40 PM

Dear Lukasz

I have done some testing with Netbotz 200 and door sensors and came to following conclusion:

In the case if Initial Netbotz unit configuration(latest firmware,thresholds configuration,trap receiver,event action) + Data Center Expert Configuration(network configuration,thresholds and alarms) have been performed accordingly, Data Center expert shows an alarm in the application in about 3-7 seconds. The difference in the range of secs is down to the overall network settings in user premises.

(CID:97484853)

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
DCIM_Support
Picard DCIM_Support
Picard

Posted: โ€Ž2020-07-02 12:55 PM . Last Modified: โ€Ž2024-04-09 11:40 PM

In response to DCIM_Support
0 Likes
0
733
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-02 12:55 PM . Last Modified: โ€Ž2024-04-09 11:40 PM

Thanks Marcis,

I should have been more specific I guess...Netbotz 200 is our ex ex Environmental Monitor and while it is called Netbotz, the name is all it has in common with Netbotz range ๐Ÿ˜€.

I am updating my question now.

(CID:97485371)

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
DCIM_Support
Picard DCIM_Support
Picard

Posted: โ€Ž2020-07-02 12:55 PM . Last Modified: โ€Ž2024-04-09 11:40 PM

0 Likes
1
734
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-02 12:55 PM . Last Modified: โ€Ž2024-04-09 11:40 PM

Hi Marcis,

 

The NetBotz appliance should post to DCE almost immediately. If it is not, take a look at the "Data Center Expert" applet in Advanced View. Is this set to post to DCE using IP or name? If it is set to name, there could be a DNS issue. Make sure the appliance can ping the DCE server by name. If it can not, even with the correct DNS, delete the entry with the name. 

 

Next, go to device, NetBotz appliance configuration, post alert data settings. Where it says "Select the Address to Use for Sending Alert Data", select the IP of the server instead of the name and click OK. This should recreate the entry in the NetBotz appliance by IP.

 

If the appliance was already posting to IP, check the logs on the bot. Create an alert and immediately afterwards, go to the unit's web page and look at http:///pages/support.html

Here, you can do things like ping and you can also hit logread to read the events. Are you getting any errors posting to the DCE server? If there is a router / firewall between the DCE and NetBotz appliance, your posts could be blocked. 

 

Steve

(CID:97484876)

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
DCIM_Support
Picard DCIM_Support
Picard

Posted: โ€Ž2020-07-02 12:55 PM . Last Modified: โ€Ž2024-04-09 11:40 PM

In response to DCIM_Support
0 Likes
0
733
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-02 12:55 PM . Last Modified: โ€Ž2024-04-09 11:40 PM

Thank you Steven, I suspect DNS name has been written into Netbotz Post configuration during the DCE discovery process so I will need to have a look on my next visit and change it to IP only. It is good to know that alarms should come through almost instantly. Thanks again.

(CID:97484879)

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
DCIM_Support
Picard DCIM_Support
Picard

Posted: โ€Ž2020-07-02 12:55 PM . Last Modified: โ€Ž2023-10-31 11:26 PM

0 Likes
0
732
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-02 12:55 PM . Last Modified: โ€Ž2023-10-31 11:26 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of