Netbotz leak detection operation and demonstration

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Netbotz leak detection operation and demonstration
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:32 AM . Last Modified: ‎2024-04-09 12:15 AM

0 Likes
8
2529
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:32 AM . Last Modified: ‎2024-04-09 12:15 AM

Netbotz leak detection operation and demonstration

My company is getting ready to purchase some Netbotz products for leak/flood notification.

  • Netbotz Rack monitor 450
  • Netbotz Rack monitor 200
  • Netbotz Leak rope sensor
  • Netbotz spot fluid sensor

 

My question is what does it take to trigger a notification?  Do these sensors need to be submerged in water or if a drop of water makes contact with the leak rope will it trigger?  I can’t seem to find any videos or demonstrations of the Netbotz products.  I’ve even reached out to the company we are buying from to furnish references to other customers who have the system installed, so I can ask their experience with the system.

 

Any help appreciated…

Tom

(CID:106203274)

Labels
  • Labels:
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:32 AM . Last Modified: ‎2024-04-09 12:15 AM

0 Likes
4
2528
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:32 AM . Last Modified: ‎2024-04-09 12:15 AM

Hi Thomas,

 

For the leak rope, you can see in the image below that the cable itself is about 1/4 inch in diameter and they are separated by an insulator that is about 1/16 of an inch:

 

For the spot leak sensors, the contacts are 1.75 (in this image, horizontal) inches and 2 inches (diagonal) apart. Sorry for the poor quality.

Steve

(CID:106203349)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 8
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:32 AM . Last Modified: ‎2024-04-09 12:15 AM

0 Likes
1
2527
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:32 AM . Last Modified: ‎2024-04-09 12:15 AM

Hi Thomas,

 

First I want to make you aware of the limitation that the NetBotz 200 does not do leak detection. It does neither spot leak nor rope leak. The 450 rack appliance can do both (1) rope leak and spot leak (2 per sensor pod including internal pod),

 

The rope leak actually has 2 wires spiraling down it's length. In order to detect a leak, enough liquid must be present to allow conductivity between the two contacts. For the spot leak sensor, you would need to have conductivity to connect any 2 of the 4 contacts on the bottom of the sensor. Please note that any liquid that does not conduct electricity such as pure water does not cause the sensor to trigger.

 

Steve

(CID:106203277)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:32 AM . Last Modified: ‎2024-04-09 12:15 AM

In response to DCIM_Support
0 Likes
0
2527
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:32 AM . Last Modified: ‎2024-04-09 12:15 AM

Yes, all sensors will connect to the 450, then 450 to 200...how far apart are the 2 wires that spiral down? also how far apart are the contacts on fluid sensor? Thanks...

(CID:106203279)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:32 AM . Last Modified: ‎2024-04-09 12:15 AM

0 Likes
4
2529
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:32 AM . Last Modified: ‎2024-04-09 12:15 AM

Hi Thomas,

 

For the leak rope, you can see in the image below that the cable itself is about 1/4 inch in diameter and they are separated by an insulator that is about 1/16 of an inch:

 

For the spot leak sensors, the contacts are 1.75 (in this image, horizontal) inches and 2 inches (diagonal) apart. Sorry for the poor quality.

Steve

(CID:106203349)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:33 AM . Last Modified: ‎2024-04-09 12:15 AM

In response to DCIM_Support
0 Likes
0
2528
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:33 AM . Last Modified: ‎2024-04-09 12:15 AM

Great...appreciate the pictures... So on the leak rope, if drops of water hit it, this may not be enough to trigger an alarm? The water would need to bridge the gap of the sensor wire...

(CID:106203388)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:33 AM . Last Modified: ‎2024-04-09 12:15 AM

In response to DCIM_Support
0 Likes
0
2527
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:33 AM . Last Modified: ‎2024-04-09 12:15 AM

Are there any corporate videos demonstrating this action?

(CID:106203389)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:33 AM . Last Modified: ‎2024-04-09 12:15 AM

In response to DCIM_Support
0 Likes
0
2527
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:33 AM . Last Modified: ‎2024-04-09 12:15 AM

Hi Thomas, That's correct, I doubt that a single drop would cause connectivity. If you look closely, you'll also see that the wires are slightly inside of the outermost points of the cable so that if it was simply damp actoss the surface that the sensor was placed on, it would also not cause connectivity. Sorry but I know of no official video demonstration.

(CID:106203390)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:33 AM . Last Modified: ‎2024-04-09 12:15 AM

In response to DCIM_Support
0 Likes
0
2527
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:33 AM . Last Modified: ‎2024-04-09 12:15 AM

Hi Thomas, I would also use a small sponge and dip it in water to make it wet so that you can keep the sponge across the leak rope sensors wires to test the water detection.

(CID:106203399)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:33 AM . Last Modified: ‎2023-10-31 11:26 PM

0 Likes
0
2527
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:33 AM . Last Modified: ‎2023-10-31 11:26 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of