Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

  • Explore the new navigation for even easier access to your community.
  • Bookmark and use our new, easy-to-remember address (community.se.com).
  • Get ready for more content and an improved experience.

Contact SchneiderCommunity.Support@se.com if you have any questions.

Close
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
84398members
353588posts

Netbotz Rack Monitor 250

EcoStruxure IT forum

A support forum for Data Center Operation, Data Center Expert, and EcoStruxure IT product users to share knowledge on installation, configuration, and general product use.

DCIM_Support
Picard
Picard
0 Likes
3
246

Netbotz Rack Monitor 250

This question was originally posted on DCIM Support by Abdul Qadir Bhatti on 2018-08-17


i am facing problem in my Netbotz Rack monitor 250 packet drop on network.

when i directly attach laptop to netbotz same packet drop and no proper communication with sensors.

please advice me how to resolve this issue.

i am using cross over cable and straight also but packet drop.

(CID:133372775)

3 Replies 3
DCIM_Support
Picard
Picard
0 Likes
0
246

Re: Netbotz Rack Monitor 250

This answer was originally posted on DCIM Support by Justine Chester on 2018-08-17


Hi Abdul,

Good day!

To properly identify the problem that you are reporting, it is best to start with identifying the behavior of the status (marked with a check and x symbol) and link (marked 10/100) LEDs on the network port. The behaviour of the LEDs should confirm whether or not the Netbotz 250 is working or not.

 

Another thing that you need to consider is whether or not a static IP address was assigned to the Netbotz 250 prior to the crossover connection attempt (I am assuming that you confirmed the dropped packets by pinging the IP address of the Netbotz appliance as this is the easiest way of doing it).

It is also a good idea to check and review how the direct/crossover cable connection was done. Feel free to use the link below for your reference:

http://www.apc.com/us/en/faqs/FA156366/

Unfortunately, it is too early to tell what is causing the Netbotz 250 to not.communicate. We might need to get additional information from you before we can provide a recommendation.

 

I hope this helps.

 

Regards,

Justine Chester

(CID:133372834)

DCIM_Support
Picard
Picard
0 Likes
0
246

Re: Netbotz Rack Monitor 250

This comment was originally posted on DCIM Support by spezialist on 2018-09-04


Dear Abdul Qadir Bhatti,

Tell us, please, have you solved this problem or not?

With respect.

(CID:134026501)