EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-02 05:28 PM . Last Modified: β2024-04-09 02:27 AM
Hi
can someone update me that Hydrogen sensor available in Netbotz APC solution? If yes what is the part number which is compatible with NBRK0570.
(CID:104174224)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-02 05:28 PM . Last Modified: β2024-04-09 02:27 AM
Hi John,
There is not specific Hydrogen sensor in the Netbotz portfolie, but you can use a Netbotz 4-20mA sensor pod. A 3rd. party Hydrogen sensor which supports 4-20mA output can be connected to Netbotz 4-20mA sensor pod and give you the data in your Netbotz 570.
Thanks
Jesper
(CID:104174231)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-02 05:28 PM . Last Modified: β2023-10-31 11:26 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.