Netbotz 250 - Modbus Register Map
  • Netbotz 250 - Modbus Register Map
129
72
dsantillan
Lieutenant dsantillan
Lieutenant
Posted: ‎2021-05-12 07:52 AM
1713
I have been trying to poll modbus data from Netbotz 250 and slave Sensor Pods 150. Main module registers work ok. Explansion modules registers do not. Using reference JLER-AFTRPH_R1 Document 990-5851A
Units are using latest firmware.
Please let me know if there is a newer map to try,
Thank you,
Douglas
  • NetBotz
TechieBala
Lieutenant JG TechieBala Lieutenant JG
Lieutenant JG
Posted: ‎2021-05-17 05:21 AM
1
1691
Hi @dsantillan Can you please try polling the Sensor Pod 150 current registers with offset of 6 and see if it helps? It appears that the modbus register map needs to be updated with the correct registers.
You may also report this issue by contacting your country technical support team.
TechieBala
Lieutenant JG
1
1692
dsantillan
Lieutenant
Posted: ‎2021-05-17 12:24 PM
In response to TechieBala
Thank you for the reply.
I decided to scan registers, indeed there is an offset of 6. Polling works having this in mind.
Best regards,
Douglas