Welcome to the new Schneider Electric Community

It's your place to connect with experts and peers, get continuous support, and share knowledge.

Close
Important Announcement: WELCOME to the new Schneider Electric Community! Community is now no longer part of Exchange, and is now rebranded under se.com. If you have any bookmarks and links saved, we request you to update them to ensure that you continue accessing our community from this new location. For any issues that you might encounter as part of this change, please reach out to SchneiderCommunity.Support@se.com, and the team will help to get your issues resolved.
Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
82514members
350118posts

Netbotz 250 - Door Switch Ports

EcoStruxure IT forum

A support forum for Data Center Operation, Data Center Expert, and EcoStruxure IT product users to share knowledge on installation, configuration, and general product use.

Solved
dsantillan
Lieutenant
Lieutenant
0 Likes
2
490

Netbotz 250 - Door Switch Ports

Hello, 

 

I am trying to connect a NBES0302 to Door 1 Switch port and also to Door 2, but the Netbotz 250 does not recognize the door switch. Firmware v6.9.6

 

If the sensor is connected to a Sensor port I see the sensor without a problem. 

 

Please indicate if there is anything that needs to be done so these two ports are activated. 

 

Thank you, 

 

Douglas

 

 

 

 

Tags (1)

Accepted Solutions
APC_Steve
Commander Commander
Commander
0 Likes
1
485

Re: Netbotz 250 - Door Switch Ports

@dsantillan ,

 

If you're connecting the door switch to the 6 "universal ports". They should indeed show up in the system. If you are connecting them to the Door 1 and Door 2 ports (#4):

 

250.PNG

You must also connect the door handles  for them to show up. Those door switches are specific to that rack access section.

 

Thanks,

Steve  

See Answer In Context

Tags (1)
2 Replies 2
APC_Steve
Commander Commander
Commander
0 Likes
1
486

Re: Netbotz 250 - Door Switch Ports

@dsantillan ,

 

If you're connecting the door switch to the 6 "universal ports". They should indeed show up in the system. If you are connecting them to the Door 1 and Door 2 ports (#4):

 

250.PNG

You must also connect the door handles  for them to show up. Those door switches are specific to that rack access section.

 

Thanks,

Steve  

Tags (1)
dsantillan
Lieutenant
Lieutenant
0 Likes
0
482

Re: Netbotz 250 - Door Switch Ports

Thank you!

Tags (1)