EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 02:41 PM . Last Modified: 2024-04-09 04:08 AM
Hello All,
Has anyone seen any issues connecting the Netbotz 200 with a Cisco 2248tp?
We have several Netbotz 200 and are struggling to get a consistent connection to a variety of Cisco 2248TP Fabric Extenders.
Some will connect straight away, some will only sync up when we force 100 Full-duplex, some will become 100 Half-Duplex and various other combinations.
Symptom is that the link light on the 2248TP does not come on and the NB200 (via Serial console) says Link Down). Plugging in to a different device the link light on the FEX works, taking the NB200 to another FEX may or may not work. Taking a working NB200 and plugging a different NB200 (same FW) wont work.
Very confused.
The FW on the Nb200 are all the same at ...
NB200: v3.7.5
AOS: v3.7.5
Thanks
Craig
(CID:99157968)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 02:41 PM . Last Modified: 2024-04-09 04:07 AM
Yes - I have had issues with a NB 450 and Symmetra ups connecting to FEX modules. Checked/tried everything. Thinking nexus bug. Ended up connecting to a catalyst with no issues.
(CID:99158147)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 02:41 PM . Last Modified: 2024-04-09 04:07 AM
I believe this is a known issue between NMC1 products and Nexus switches, where the NMC will continually fail to negotiate to 100/F no matter what switch port or NMC setting is used. We see this issue on literally hundreds of devices, and have had to resort to placing NMC1 devices on 48-port unmanaged switch/hubs that can deal with 10/H and 100/H just to get comms consistency.
(CID:99157995)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 02:41 PM . Last Modified: 2024-04-09 04:07 AM
Dear Craig Oberg
(CID:101613711)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 02:41 PM . Last Modified: 2023-10-31 11:23 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.