NetBotz Wireless OID Identification for NBWS100H

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • NetBotz Wireless OID Identification for NBWS100H
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
109
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
62
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:59 AM . Last Modified: ‎2024-04-09 12:06 AM

0 Likes
6
1268
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:59 AM . Last Modified: ‎2024-04-09 12:06 AM

NetBotz Wireless OID Identification for NBWS100H

Hi Team,

Our customer wants to integrate NetBotz 570 & NBWS100H sensors with their SNMP Monitoring system environment.

There question is how they can identify each NBWS100H sensor with OID Index for wireless, such as 1.3.6.1.4.1.5528.100.4.1.1.1.2.3829175974.

Last 10 numbers, 3829175974, seems to the identifier, but cannot find this number by Advanced View or any wireless information.  Does it match with either Serial number, MAC Address, or any information?

best regards,

Yoshi

(CID:106204617)

Labels
  • Labels:
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:59 AM . Last Modified: ‎2024-04-09 12:06 AM

0 Likes
3
1268
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:59 AM . Last Modified: ‎2024-04-09 12:06 AM

Hi Yoshi,

 

What the customer should do is give each sensor a label. Make sure each label is unique . This is pretty much the same as any other temperature sensor and polling it via SNMP.

You would then poll:

netBotzAPC.netBotz.netBotzSensors.netBotzNumericSensors.tempSensorTable.tempSensorEntry.tempSensorLabel

With that label, pay attention to the SNMP instance returned. The last digits you referred to as an identifier is actually the SNMP instance.

You will notice that the sensor: Yoshi-Temperature has an instance of 3710249732

You then want to poll for the actual temperature. Here I'm using:

netBotzAPC.netBotz.netBotzSensors.netBotzNumericSensors.tempSensorTable.tempSensorEntry.tempSensorValueIntF

(there are other options)

 

 

Note that the 2nd value from the bottom has a matching instance of 3710249732 and a value of 71 which matches the current value for that sensor in AV:


Steve

 

(CID:106204663)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 6
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:59 AM . Last Modified: ‎2024-04-09 12:06 AM

0 Likes
3
1269
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:59 AM . Last Modified: ‎2024-04-09 12:06 AM

Hi Yoshi,

 

What the customer should do is give each sensor a label. Make sure each label is unique . This is pretty much the same as any other temperature sensor and polling it via SNMP.

You would then poll:

netBotzAPC.netBotz.netBotzSensors.netBotzNumericSensors.tempSensorTable.tempSensorEntry.tempSensorLabel

With that label, pay attention to the SNMP instance returned. The last digits you referred to as an identifier is actually the SNMP instance.

You will notice that the sensor: Yoshi-Temperature has an instance of 3710249732

You then want to poll for the actual temperature. Here I'm using:

netBotzAPC.netBotz.netBotzSensors.netBotzNumericSensors.tempSensorTable.tempSensorEntry.tempSensorValueIntF

(there are other options)

 

 

Note that the 2nd value from the bottom has a matching instance of 3710249732 and a value of 71 which matches the current value for that sensor in AV:


Steve

 

(CID:106204663)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:59 AM . Last Modified: ‎2024-04-09 12:06 AM

In response to DCIM_Support
0 Likes
0
1268
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:59 AM . Last Modified: ‎2024-04-09 12:06 AM

Hi Steve, Thank you for the detailed reply. I will share your response to our customer and partner. best regards, Yoshi

(CID:106204685)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:59 AM . Last Modified: ‎2024-04-09 12:06 AM

In response to DCIM_Support
0 Likes
0
1268
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:59 AM . Last Modified: ‎2024-04-09 12:06 AM

Hi Yoshi, You may want to use this OID instead of the INT OID mentioned above....just more accurate: netBotzAPC.netBotz.netBotzSensors.netBotzNumericSensors.tempSensorTable.tempSensorEntry.tempSensorValue Steve

(CID:106204798)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:59 AM . Last Modified: ‎2024-04-09 12:06 AM

In response to DCIM_Support
0 Likes
0
1268
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:59 AM . Last Modified: ‎2024-04-09 12:06 AM

Hi Steve, Thank you for the advice. Partner said ".iso.org.dod.internet.private.enterprises.netBotzAPC.netBotz.netBotzSensors.netBotzNumericSensors.tempSensorTable.tempSensorEntry.tempSensorValue" value seems to be more accurate than "netBotzAPC.netBotz.netBotzSensors.netBotzNumericSensors.tempSensorTable.tempSensorEntry.tempSensorValue" because they are include decimal value. They would assign this OID but the 3rd vendor software and still indetify each sensor by index. They also would like to know the possibility whether the index value change in the daily use and operation such as reboot, device add, and back up restore to the same appliacen with same devices, including wireless 100 series. Could you get the confirmation whenter index will not be changed or changed? best regards, Yoshi

(CID:106205553)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:59 AM . Last Modified: ‎2024-04-09 12:06 AM

0 Likes
0
1268
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:59 AM . Last Modified: ‎2024-04-09 12:06 AM

Hi Yoshi,

 

The instance of the OID remains static as long as the sensor is connected and the appliance is not reset to defaults. This value should not change over time or due to a reboot. I'm using the answer here as the comment does not allow for images to be embedded. Please note that the Yoshi-temperature sensor still has the same instance as when I initially posted my response and we use that system regularly for troubleshooting and testing (I'm actually surprised the name is still there).

 

 

Steve

(CID:106205586)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:59 AM . Last Modified: ‎2023-10-31 11:27 PM

0 Likes
0
1268
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:59 AM . Last Modified: ‎2023-10-31 11:27 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of