NetBotz Dry Contact connection to Fire Alarm Panel, Generator or AC

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forΒ 
ShowΒ Β onlyΒ  | Search instead forΒ 
Did you mean:Β 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • NetBotz Dry Contact connection to Fire Alarm Panel, Generator or AC
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
108
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
62
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 01:22 AM . Last Modified: β€Ž2024-04-05 04:10 AM

0 Likes
7
2373
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 01:22 AM . Last Modified: β€Ž2024-04-05 04:10 AM

NetBotz Dry Contact connection to Fire Alarm Panel, Generator or AC

Hi,

Any advise on connecting NetBotz 570 to external equipment e.g. fire alarm panel, generator or AC dry contacts, specifically on conditions the equipment contacts must fulfill?

(CID:126170428)

Labels
  • Labels:
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 01:22 AM . Last Modified: β€Ž2024-04-05 04:10 AM

0 Likes
2
2373
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 01:22 AM . Last Modified: β€Ž2024-04-05 04:10 AM

Dear pzodawa and team,

From my own practical experience: there are no problems or special recommendations. If you mean NetBotz Dry Contact Cable - 15 ft. (NBES0304), the external equipment (e.g. fire alarm panel, generator or AC dry contacts) should simply have low-voltage dry contacts (NC or NO), that are able to switching the load max ~5V/0.5mA.

The time for the presence of dry contacts in the closed or open state must be at least >200mS. Otherwise, NetBotz device simply does not detect changes in the status of dry contacts. This is described in the following documents on the NetBotz device:

  • NetBotz Rack Monitor 200 - Installation and Quick Configuration Manual - on page 23;
  • NetBotz Rack Monitor 450/550/570 Installation and Quick Configuration Manual - on page 28;
  • NetBotz Rack Monitor 250 - Installation and Quick Configuration Guide - on page 30.

The active resistance of the dry contacts (excluding active resistance NetBotz Dry Contact Cable - 15 ft. (NBES0304)) should be no more than <9kOhm, so that the NetBotz device reliably determines the closed state of the dry contacts.

Similarly, the active resistance of dry contacts (excluding active resistance NetBotz Dry Contact Cable - 15 ft. (NBES0304)) must be at least >11kOhm so that the NetBotz device reliably detects the open state of the dry contacts.

This should be taken into account in special cases, when dry contacts are connected to a NetBotz device using an extension cable, for example, a structured cabling system of the building, fireproof cables for fire panels and the like.

In addition, in all cases, it is recommended to attach a ferritic bead to the external sensor cable as close to the NetBotz device as possible, for  EMI suppression.

And the last recommendation for the use of extension cables for external sensors and, in particular, for using NetBotz Dry Contact Cable - 15 ft. (NBES0304). You should always try to connect NetBotz Dry Contact Cable - 15 ft. (NBES0304) directly to the sensor port of the NetBotz device, i.e.:

NetBotz (sensor port) <-- NBES0304 cable --> 3rd party extension cable / patch panel, etc. <-- dry contact in external equipment

And you should try to avoid connecting NetBotz Dry Contact Cable - 15 ft. (NBES0304) to the sensor port NetBotz device via an extension cable, i.e. like this:

NetBotz (sensor port) --> 3rd party extension cable / patch panel, etc. <-- NBES0304 cable --> dry contact in external equipment

This is due to the fact that the RJ-45 connectors of external sensors have some radio components responsible for the correct identification of the sensor in the NetBotz device. If this is not understood, then, under certain circumstances, strange problems can really appear, for example, as Sven Ortmann described in his question .

I am glad to answer your questions.

(CID:126170441)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 7
DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 01:22 AM . Last Modified: β€Ž2024-04-05 04:10 AM

0 Likes
2
2374
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 01:22 AM . Last Modified: β€Ž2024-04-05 04:10 AM

Dear pzodawa and team,

From my own practical experience: there are no problems or special recommendations. If you mean NetBotz Dry Contact Cable - 15 ft. (NBES0304), the external equipment (e.g. fire alarm panel, generator or AC dry contacts) should simply have low-voltage dry contacts (NC or NO), that are able to switching the load max ~5V/0.5mA.

The time for the presence of dry contacts in the closed or open state must be at least >200mS. Otherwise, NetBotz device simply does not detect changes in the status of dry contacts. This is described in the following documents on the NetBotz device:

  • NetBotz Rack Monitor 200 - Installation and Quick Configuration Manual - on page 23;
  • NetBotz Rack Monitor 450/550/570 Installation and Quick Configuration Manual - on page 28;
  • NetBotz Rack Monitor 250 - Installation and Quick Configuration Guide - on page 30.

The active resistance of the dry contacts (excluding active resistance NetBotz Dry Contact Cable - 15 ft. (NBES0304)) should be no more than <9kOhm, so that the NetBotz device reliably determines the closed state of the dry contacts.

Similarly, the active resistance of dry contacts (excluding active resistance NetBotz Dry Contact Cable - 15 ft. (NBES0304)) must be at least >11kOhm so that the NetBotz device reliably detects the open state of the dry contacts.

This should be taken into account in special cases, when dry contacts are connected to a NetBotz device using an extension cable, for example, a structured cabling system of the building, fireproof cables for fire panels and the like.

In addition, in all cases, it is recommended to attach a ferritic bead to the external sensor cable as close to the NetBotz device as possible, for  EMI suppression.

And the last recommendation for the use of extension cables for external sensors and, in particular, for using NetBotz Dry Contact Cable - 15 ft. (NBES0304). You should always try to connect NetBotz Dry Contact Cable - 15 ft. (NBES0304) directly to the sensor port of the NetBotz device, i.e.:

NetBotz (sensor port) <-- NBES0304 cable --> 3rd party extension cable / patch panel, etc. <-- dry contact in external equipment

And you should try to avoid connecting NetBotz Dry Contact Cable - 15 ft. (NBES0304) to the sensor port NetBotz device via an extension cable, i.e. like this:

NetBotz (sensor port) --> 3rd party extension cable / patch panel, etc. <-- NBES0304 cable --> dry contact in external equipment

This is due to the fact that the RJ-45 connectors of external sensors have some radio components responsible for the correct identification of the sensor in the NetBotz device. If this is not understood, then, under certain circumstances, strange problems can really appear, for example, as Sven Ortmann described in his question .

I am glad to answer your questions.

(CID:126170441)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 01:22 AM . Last Modified: β€Ž2024-04-05 04:10 AM

In response to DCIM_Support
0 Likes
0
2373
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 01:22 AM . Last Modified: β€Ž2024-04-05 04:10 AM

Dear spezialist,

You have pretty much answered my question. Thanks for the prompt response, much appreciated!

 

(CID:126170788)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 01:22 AM . Last Modified: β€Ž2024-04-05 04:10 AM

In response to DCIM_Support
0 Likes
0
2373
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 01:22 AM . Last Modified: β€Ž2024-04-05 04:10 AM

I am glad to answer your questions πŸ˜€.

(CID:126171011)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 01:22 AM . Last Modified: β€Ž2024-04-05 04:10 AM

0 Likes
0
2373
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 01:22 AM . Last Modified: β€Ž2024-04-05 04:10 AM

Hi pzodawa

As spezialist mentioned the Netbotz dry contact cable will work perfectly. I have this setup and working to provide fire alarm panel notifications such as 'manual mode' or 'stage 2 suppression gas release.'

A MODBUS connection to the 570 would provide you much more information for your generator than dry contact. However, your facilities team may wish to use any MODBUS card to connect to their Building Management System (BMS). I have my generator using dry contact to DCE reporting on low fuel, generator running on load, common alarm and low battery charge. The MODBUS then goes to our maint team who operate and support the generator via the BMS.

(CID:126171847)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 01:22 AM . Last Modified: β€Ž2024-04-05 04:10 AM

0 Likes
1
2373
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 01:22 AM . Last Modified: β€Ž2024-04-05 04:10 AM

Just to add on great inputs from spezialist and scott.sexton; for dry contact, I would recommend to use a normally closed (NC) contact instead of normally open.

That way, you'll get notified in the event the cable break.

 

On some fire panel, as mentioned above, these panel will typically have several dry contact outputs, i.e 1st stage, 2nd stage  and panel fault etc. Suggest to monitor these using individual dry contacts, to get clarity on the alarm.

 

If you need  a large amount of dry contact input, it might be easier to use Netbotz with sealevel I/O, where you can install the sealevel terminal block kit inside a dedicated panel.

 

As for genset, yes, if you need more details like fuel level, output voltage, etc, those are typically via modbus.

(CID:126172240)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 01:23 AM . Last Modified: β€Ž2024-04-05 04:10 AM

In response to DCIM_Support
0 Likes
0
2373
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 01:23 AM . Last Modified: β€Ž2024-04-05 04:10 AM

Since this topic was interesting for the community, I supplemented my answer so that it was detailed and complete.

Always happy to answer questions πŸ˜€.

(CID:126172414)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: β€Ž2020-07-04 01:23 AM . Last Modified: β€Ž2023-10-22 03:13 AM

0 Likes
0
2373
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: β€Ž2020-07-04 01:23 AM . Last Modified: β€Ž2023-10-22 03:13 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Β© 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of