NetBotz 750 with GSM Modem

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • NetBotz 750 with GSM Modem
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
Sreng
Crewman Sreng
Crewman

Posted: ‎2021-06-21 02:27 AM

0 Likes
4
3047
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-21 02:27 AM

NetBotz 750 with GSM Modem

Dear Everyone,

 

I have one question relate to the new model of NetBotz 750, does NetBotz 750 support GSM MultiTech model : MTD-H5 ?

 

Regards,

SRENG

Labels
  • Labels:
  • NetBotz
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
APC_Steve
Captain APC_Steve Captain
Captain

Posted: ‎2021-06-22 05:15 AM

In response to Sreng
1 Like
0
3027
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-22 05:15 AM

Hi @Sreng 

 

As I mentioned, there is no modem option. The only options are e-mail to a cell phone number and that only through normal network e-mail or something like the gateway I mentioned.

 

Steve

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-22 05:24 AM

In response to Sreng
1 Like
0
3024
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-22 05:24 AM

Hi @Sreng ,

 

You might want to consider an email to SMS service for now. There is a good chance that the 750 will support GSMs in the next firmware release. This way you can then cancel your email to sms service once the 750 supports GSMs.

 

Kevin

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
APC_Steve
Captain APC_Steve Captain
Captain

Posted: ‎2021-06-21 05:17 AM

0 Likes
3
3041
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-21 05:17 AM

Hi @Sreng ,

 

Sorry, no. The NetBotz 750/755 do not support connecting modems directly to the unit. An option you may want to try is an e-mail gateway such as the one here:
https://www.intwineconnect.com/services/lte-failover

 

Thanks,

Steve

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Sreng
Crewman Sreng
Crewman

Posted: ‎2021-06-22 05:04 AM

In response to APC_Steve
0 Likes
2
3030
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-22 05:04 AM

Hello @Steve,

 

Thank for your email, do we have any other options that able to use NetBotz 750 to sent SMS to any telephone number?

or only one option available is sending email? 

 

Regards,

SRENG

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

APC_Steve
Captain APC_Steve Captain
Captain

Posted: ‎2021-06-22 05:15 AM

In response to Sreng
1 Like
0
3028
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-22 05:15 AM

Hi @Sreng 

 

As I mentioned, there is no modem option. The only options are e-mail to a cell phone number and that only through normal network e-mail or something like the gateway I mentioned.

 

Steve

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Anonymous user
Not applicable

Posted: ‎2021-06-22 05:24 AM

In response to Sreng
1 Like
0
3025
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2021-06-22 05:24 AM

Hi @Sreng ,

 

You might want to consider an email to SMS service for now. There is a good chance that the 750 will support GSMs in the next firmware release. This way you can then cancel your email to sms service once the 750 supports GSMs.

 

Kevin

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of