Posted: 2023-05-22 06:45 AM
Bonjour, je souhaite piloter plusieurs relais (3) en cas de température trop élevé ou détection de fumée.
Est-il possible d'ajouter un module Sealevel comme sur les NetBotz 550, ou cela ne fonctionne pas ?
Ou avez vous des produits a me recommander ?
En vous remerciant par avance.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-05-22 06:54 AM
Hello @ValRdgs ,
The subject line mentions the NetBotz 250 but the body (and your last comment in another post) mentions the NetBotz 550. The 250 can not use the sealevel device and has no options for adding output relays.
The V3 NetBotz such as the 550 however can work wih sealevel devices. The user manual:
Notes this on page 50 and beyond.
Sealevel also mentions this on their web page:
https://www.sealevel.com/support/how-can-i-expand-the-digital-io-in-my-apc-netbotz-appliance/
I believe the 2 mentioned are the only ones that worked but please note these have not been tested in years (at least not by us) and newer firmware on the 550 or the Sealevel device could change how they work together.
Thanks,
Steve
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-05-22 06:54 AM
Hello @ValRdgs ,
The subject line mentions the NetBotz 250 but the body (and your last comment in another post) mentions the NetBotz 550. The 250 can not use the sealevel device and has no options for adding output relays.
The V3 NetBotz such as the 550 however can work wih sealevel devices. The user manual:
Notes this on page 50 and beyond.
Sealevel also mentions this on their web page:
https://www.sealevel.com/support/how-can-i-expand-the-digital-io-in-my-apc-netbotz-appliance/
I believe the 2 mentioned are the only ones that worked but please note these have not been tested in years (at least not by us) and newer firmware on the 550 or the Sealevel device could change how they work together.
Thanks,
Steve
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-05-22 07:27 AM
Je te remercie pour la confirmation, dommage....
Aurais tu des solution autre afin de pouvoir gerer ces relais ?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-05-22 07:30 AM
Sorry @ValRdgs but no. The 250 does not have options for this. Hopefully when you contacted tech support directly, they informed you of this.
Steve
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-05-22 08:38 AM
Pas de problème, merci beaucoup Steve pour toutes tes réponses, clair et très rapide!!