Posted: 2023-01-16 05:20 AM
NetBotz 250 - PRTG Sensors reporting false values for Temp and Humidity since NetBotz Firmware update
Since upgrading the firmware on our NetBotz 250 devices the snmp PRTG Sensors are reporting -1% for Humidity and 0 for Temperature for all of our devices but Data Centre Expert is reporting the correct values.
Firmware Updated from App v6.8.0, AOS 6.8.2, Boot v1.0.8 to App v7.0.6, AOS v7.0.6, Boot v1.0.8 Network Management Card Model Number AP9538.
Sensors OID 1.3.6.1.4.1.318.1.1.10.3.13.1
Humidity 1.3.6.1.4.1.318.1.1.10.3.13.1.1.6
Temperature 1.3.6.1.4.1.318.1.1.10.3.13.1.1.3
Has anyone else had this issue or similar? All the NetBotz are affected and I am unable to find a copy of the previous firmware to roll back.
- Labels:
-
NetBotz
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-01-16 05:35 AM
What kind of sensors you have ?
Wireless Zigbee of RJ45 connection
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-01-16 07:57 AM
They are the Wired RJ45 Sensors
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-01-16 08:18 AM . Last Modified: 2023-01-16 08:19 AM
please try:
Sensors OID .1.3.6.1.4.1.318.1.1.10.1.3.3.1
Humidity 1.3.6.1.4.1.318.1.1.10.1.3.3.1.6
Temperature 1.3.6.1.4.1.318.1.1.10.1.3.3.1.4
read from powernet441.mib
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-01-16 09:56 AM . Last Modified: 2023-01-16 09:56 AM
Hi @mr12,
The ..318.1.1.10 OIDs are legacy support for the old APC Environmental Monitors (old units from about the era when someone decided modern electronics shouldn't be beige!). It appears this legacy support is drying up.
You should find what you're looking for under the .1.3.6.1.4.1.318.1.1.25.1 tree, which is intended for these UIO sensors. Examples from one I have here:
.1.3.6.1.4.1.318.1.1.25.1.2.1.1.1.1 = INTEGER: 1 (uioSensorStatusPortID)
.1.3.6.1.4.1.318.1.1.25.1.2.1.2.1.1 = INTEGER: 1 (uioSensorStatusSensorID)
.1.3.6.1.4.1.318.1.1.25.1.2.1.3.1.1 = STRING: "Port 1 Temp 1" (uioSensorStatusSensorName)
.1.3.6.1.4.1.318.1.1.25.1.2.1.4.1.1 = STRING: "Port 1" (uioSensorStatusSensorLocation)
.1.3.6.1.4.1.318.1.1.25.1.2.1.5.1.1 = INTEGER: 68 (uioSensorStatusTemperatureDegF)
.1.3.6.1.4.1.318.1.1.25.1.2.1.6.1.1 = INTEGER: 20 (uioSensorStatusTemperatureDegC)
.1.3.6.1.4.1.318.1.1.25.1.2.1.7.1.1 = INTEGER: -1 (uioSensorStatusHumidity; this isn't a THM so -1 means not available)
.1.3.6.1.4.1.318.1.1.25.1.2.1.8.1.1 = INTEGER: 0 (uioSensorStatusViolationStatus)
.1.3.6.1.4.1.318.1.1.25.1.2.1.9.1.1 = INTEGER: 1 (uioSensorStatusAlarmStatus)
.1.3.6.1.4.1.318.1.1.25.1.2.1.10.1.1 = INTEGER: 2 (uioSensorStatusCommStatus, 2=OK)
And for each of these, replace the final .1.1 with .2.1 for the second built-in UIO port.
Link copied. Please paste this link to share this article on your social media post.
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-01-17 11:08 AM
Do you use the NetBotz 250 devices?
Link copied. Please paste this link to share this article on your social media post.