EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 05:15 PM . Last Modified: 2024-04-04 11:58 PM
i want to add surveillance system in my data center that integrated with NetBotz 150 please help me out?
(CID:130683396)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 05:15 PM . Last Modified: 2024-04-04 11:58 PM
Hi Abdul.
First, the NetBotz 150 is a sensor pod. There is no camera and it can not be used in surveillance. The NetBotz 160 camera pod would need to be used in conjunction with a base NetBotz 4xx or 5xx device. The 355 has an onboard camera but can not connect to a pod.
Please also note that neither sensor pod nor camera pod are IP addressable. You can not put them on the network by themselves. They must have a compatible NetBotz appliance to which they are connected.
Thanks,
Steve.
(CID:130683402)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 05:15 PM . Last Modified: 2024-04-04 11:58 PM
Hi Abdul.
First, the NetBotz 150 is a sensor pod. There is no camera and it can not be used in surveillance. The NetBotz 160 camera pod would need to be used in conjunction with a base NetBotz 4xx or 5xx device. The 355 has an onboard camera but can not connect to a pod.
Please also note that neither sensor pod nor camera pod are IP addressable. You can not put them on the network by themselves. They must have a compatible NetBotz appliance to which they are connected.
Thanks,
Steve.
(CID:130683402)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 05:15 PM . Last Modified: 2024-04-04 11:58 PM
ok
Thank you.
(CID:131961105)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 05:15 PM . Last Modified: 2023-10-22 03:11 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.