NBWS100T fails to connect to NBRK0570 following Firmware transfer

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • NBWS100T fails to connect to NBRK0570 following Firmware transfer
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
126
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:26 AM . Last Modified: ‎2024-04-08 11:39 PM

0 Likes
4
591
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:26 AM . Last Modified: ‎2024-04-08 11:39 PM

NBWS100T fails to connect to NBRK0570 following Firmware transfer

Upon completion of firmware transfer and status change to "Ready to apply" followed by Apply Firmware Update, all sensors dropped off as pod unplugged. Sensors have been powered off and on but will not connect to the NetBotz appliance. NetBotz AV shows all sensors in "Ready to apply" status as unplugged. This appears to be happening across all our NetBotz appliances with multiple sensors going offline.

What options are available for verification the firmware upgrade was successfully if AV can not connect to sensor.  Can sensors be hardwired to the NetBotz (port on top of sensor).      

NBRK0570 Bootstrap version:   4.5.1 (Build: 20151117_1714)
Sensor Pod 150 Integrated Bootstrap version:   3.010
Sensor Pod 100 T and H Application version:   1.0.0
NetBotz AV Version:   4.5.1 (Build: AV_20151125_1258)

 

 

(CID:106210644)

Labels
  • Labels:
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:26 AM . Last Modified: ‎2024-04-08 11:39 PM

0 Likes
2
591
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:26 AM . Last Modified: ‎2024-04-08 11:39 PM

Hi Barry,

 

How long have the sensors been connected? Have they been working OK prior to the attempted update? Have there been any previous issues? I have seen issues with the initial firmware if the sensors have had communications issues and reboot multiple times to attempt to reconnect.


To verify this issue, set the NetBotz global log level to alert and set the wireless log level to trace (return them after the test). Remove one of the sensors from the bot. Configure the NetBotz appliance for autojoin and reboot the wireless sensor and put it in close proximity to the coordinator. Allow autojoin to run for a few minutes. If you look at the NetBotz logs, you shouldsee the mac addresses of the wireless sensors attempting to join the network. If you do not see the actual mac of the wireless sensor but instead see something perhaps with all zeros, this is likely the issue. Here is an example of what the logs may look like:

Jun 6 11:33:16 netbotz304 daemon.info nbArgusDaemon: [SN0] 000000000000: isZeroSN 13943
Jun 6 11:33:16 netbotz304 daemon.warn nbArgusDaemon: [SDP][SN0] Rejecting Node [00124B00043E4068] for invalid serial number 


If you see this issue, please contact tech support directly and note this post.


Steve

(CID:106210662)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:26 AM . Last Modified: ‎2024-04-08 11:39 PM

In response to DCIM_Support
0 Likes
0
591
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:26 AM . Last Modified: ‎2024-04-08 11:39 PM

Hi Steve,  thanks for responding to my post. I did see the same entries in the NetBotz log. (see below)

Jul 22 15:22:50 netbotz8F6E25 daemon.info nbArgusDaemon: [SN0] 000000000000: isZeroSN 13945 Jul 22 15:22:50 netbotz8F6E25 daemon.warn nbArgusDaemon: [SDP][SN0] Rejecting Node [00124B00044085B8] for invalid serial number

(CID:106891175)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:27 AM . Last Modified: ‎2024-04-08 11:39 PM

In response to DCIM_Support
0 Likes
0
591
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:27 AM . Last Modified: ‎2024-04-08 11:39 PM

Thanks Barry, Copy those logs and as I mentioned, call support and mention this post and provide them with the logs. Steve.

(CID:106891176)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 04:27 AM . Last Modified: ‎2023-10-31 11:23 PM

0 Likes
0
591
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 04:27 AM . Last Modified: ‎2023-10-31 11:23 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore