NBRK0570 powers on and switches back off

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • NBRK0570 powers on and switches back off
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:51 AM . Last Modified: ‎2024-04-09 12:09 AM

0 Likes
10
833
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:51 AM . Last Modified: ‎2024-04-09 12:09 AM

NBRK0570 powers on and switches back off

Hi Team,

I am not sure if anyone here has experienced this, I have a NetBotz 570 which powers on and switches back off repeatedly. I can hear the relay inside switching, this therefore doesn't allow the NetBotz time to boot in order for me to login to the appliance.

This is the second NetBotz am seeing this and I can't actually seem to find the remedy for this.

Regards,

Felix

(CID:106204237)

Labels
  • Labels:
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 10
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:52 AM . Last Modified: ‎2024-04-09 12:09 AM

0 Likes
8
833
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:52 AM . Last Modified: ‎2024-04-09 12:09 AM

Hi Felix,

 

Is this unit plugged into 120v? 230v? Has this just begun happening? Have you done any troubleshooting such as disconnecting pods, trying a different power source, disconnecting network jack, etc? How old is the unit? Is it under warranty?

If you've tried different power options and disconnected other things that could themselves be helping cause this issue, it is likely the unit needs replacing. 

 

Steve

(CID:106204242)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:52 AM . Last Modified: ‎2024-04-09 12:09 AM

In response to DCIM_Support
0 Likes
0
833
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:52 AM . Last Modified: ‎2024-04-09 12:09 AM

Hi Felix, What region are you in? Have you spoken to tech support directly? If so, to whom? Do you have a case#?

(CID:106204252)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:52 AM . Last Modified: ‎2024-04-09 12:09 AM

In response to DCIM_Support
0 Likes
0
833
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:52 AM . Last Modified: ‎2024-04-09 12:09 AM

Hi Steve, Apologies for the late response as the site is outside the country and I have limited access to the internet. This is connected to an APC Switched Rack PDU with 230v, I have removed pods, sensors and modem but still has the same issue. Actually what happens is that, after removing the power cord for a while, on plugging in it works fine for about 5 to 10mins but then it begins switching on and off until I plug the power cord off again for a while. This problem started almost 1hr after installing the NetBotz for the first time. I had to upgrade the netbotz to v4.5.0 from it's default v4.3.0 just to confirm it's not a hardware issue but then I am convinced it's the hardware issue. I am from Kenya but the site is in Ethiopia, I haven't talked to any tech support yet and equally don't have a case#. I am yet to do this when I get back to Kenya as I had to be sure of the issue. Thank you. Regards, Felix

(CID:106204344)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:52 AM . Last Modified: ‎2024-04-09 12:09 AM

In response to DCIM_Support
0 Likes
0
833
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:52 AM . Last Modified: ‎2024-04-09 12:09 AM

Thanks Felix, I't looking like it should be replaced and if you could ask the tech support rep to see if he can get it replaced and get the old unit back to me, I'd like to see if I can send it on to our engineering team. Note this thread if necessary. Steve

(CID:106204345)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:52 AM . Last Modified: ‎2024-04-09 12:09 AM

In response to DCIM_Support
0 Likes
0
833
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:52 AM . Last Modified: ‎2024-04-09 12:09 AM

Hi Steve, Thank you for your prompt response, Ethiopia is really frustrating to move goods in and out of the country. Nevertheless I shall do my best. I also mention we have another NetBotz 570 in stock back in our Kenya office. It had the same issue just before I left for this site should I do the same for it? I was hoping to check on it when I get back but now I feel I have options left. Regards, Felix.

(CID:106204346)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:52 AM . Last Modified: ‎2024-04-09 12:09 AM

In response to DCIM_Support
0 Likes
0
833
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:52 AM . Last Modified: ‎2024-04-09 12:09 AM

Hi Felix, If you have done similar testing, I would think it's a similar issue as well. Steve

(CID:106204347)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:52 AM . Last Modified: ‎2024-04-09 12:08 AM

In response to DCIM_Support
0 Likes
0
833
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:52 AM . Last Modified: ‎2024-04-09 12:08 AM

Hi Steve, Well noted and thank you. Regards, Felix.

(CID:106204349)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:52 AM . Last Modified: ‎2024-04-09 12:08 AM

In response to DCIM_Support
0 Likes
0
833
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:52 AM . Last Modified: ‎2024-04-09 12:08 AM

Hi Steve, Thank you, I did receive the warranty unit only that I am not sure the procedure to follow in transfer of the current NetBotz Device Monitoring Pack license from the faulty NetBotz to the new warranty NetBotz. Regards, Felix

(CID:106205157)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:53 AM . Last Modified: ‎2024-04-09 12:08 AM

In response to DCIM_Support
0 Likes
0
833
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:53 AM . Last Modified: ‎2024-04-09 12:08 AM

Hi Steve, Thank you, I was assisted on the transfer of the license and now everything is fine. Regards, Felix.

(CID:106206088)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 02:53 AM . Last Modified: ‎2023-10-31 11:23 PM

0 Likes
0
833
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 02:53 AM . Last Modified: ‎2023-10-31 11:23 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore