NBRK0200 and NBRK0250: mix sensor pods and temperature sensors?

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • NBRK0200 and NBRK0250: mix sensor pods and temperature sensors?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:19 AM . Last Modified: ‎2024-04-08 02:35 AM

0 Likes
4
764
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:19 AM . Last Modified: ‎2024-04-08 02:35 AM

NBRK0200 and NBRK0250: mix sensor pods and temperature sensors?

Hi all!

Whether it is possible to mix sensor pods and temperature/humidity sensors  at connection to same NBRK0200 or NBRK0250?

What at the same time there can be a maximum number of cascade devices?

Here excerpts from the corresponding instructions, where about it it isn't absolutely accurately written:

NBRK0200

"You can cascade to A-Link ports up to twelve NetBotz Rack Sensor Pod 150s (NBPD0150) and up to a combined total of eight Temperature Sensors with Digital Display (AP9520T) and Temperature/Humidity Sensors with Digital Display (AP9520TH). You cannot cascade NetBotz 200s."

NBRK0250

"You can cascade up to six NetBotz Rack Sensor Pod 150s (NBPD0150) and up to eight Temperature Sensors with Digital Display (AP9520T) and Temperature/Humidity Sensors with Digital Display (AP9520TH) to A-Link ports. You cannot cascade Rack Monitor 250s or other NetBotz appliances."

Very thanks for the support.

(CID:110020412)

Labels
  • Labels:
  • NetBotz
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:19 AM . Last Modified: ‎2024-04-08 02:35 AM

0 Likes
2
766
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:19 AM . Last Modified: ‎2024-04-08 02:35 AM

Hi Spezialist,

 

Yes, you can add all the sensors / pods at the same time. The limit to the number of sensor pods does not effect the limit of the number of A-link temp/humidity sensors that you can add. You can add the full compliment of both at the same time.


Steve

(CID:110020441)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:19 AM . Last Modified: ‎2024-04-08 02:35 AM

0 Likes
2
767
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:19 AM . Last Modified: ‎2024-04-08 02:35 AM

Hi Spezialist,

 

Yes, you can add all the sensors / pods at the same time. The limit to the number of sensor pods does not effect the limit of the number of A-link temp/humidity sensors that you can add. You can add the full compliment of both at the same time.


Steve

(CID:110020441)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:19 AM . Last Modified: ‎2024-04-08 02:35 AM

In response to DCIM_Support
0 Likes
0
766
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:19 AM . Last Modified: ‎2024-04-08 02:35 AM

Hi Steven Marchetti,

I.e., for

-- NBRK0200 it is possible to connect at the same time twelve sensor pods plus eight temperature/humidity sensors;

-- NBRK0250 it is possible to connect at the same time six sensor pods plus eight temperature/humidity sensors.

It is correct?

Very thanks for the support.

(CID:110791500)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:20 AM . Last Modified: ‎2024-04-08 02:35 AM

In response to DCIM_Support
0 Likes
0
766
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:20 AM . Last Modified: ‎2024-04-08 02:35 AM

Hi Spezialist,


Yes, those are the numbers.


Steve

(CID:110791502)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 10:20 AM . Last Modified: ‎2023-10-22 03:07 AM

0 Likes
0
764
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 10:20 AM . Last Modified: ‎2023-10-22 03:07 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore