Posted: 2020-07-05 10:42 PM . Last Modified: 2024-04-03 12:23 AM
Following installation of Netbotz rack access, the HID cards that shipped with the handles are not getting recognised. No beep, no entry in the unregistered cards table on the UI? Any ideas? Firmware on appliance has been updated to
(CID:149784379)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 10:42 PM . Last Modified: 2024-04-03 12:23 AM
Dear Kevin Kolobe,
Please tell us, were you able to solve your problem or not?
With respect.
(CID:151062331)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 10:42 PM . Last Modified: 2024-04-03 12:23 AM
Hi spezialist,
I was able to resolve the issue. It was a faulty 250 appliance. I ran tests on a different appliance and the same handles were able to recognize the cards and allow them access. Appliance was replaced under warranty and solution is up and running.
Regards
(CID:151062439)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 10:42 PM . Last Modified: 2024-04-03 12:23 AM
Ok, very thanks for the good feedback.
(CID:151062447)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 10:42 PM . Last Modified: 2023-10-22 03:07 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
Welcome to your new personalized space.
of