I imported "Motivair Chilled Door"DDF for my DCE.
However, my ChilledDoor M12 Model is not recognized.
What should I check?
https://ddf.ecostruxureit.com/view/Chilled%20Door/Motivair
I attached the SNMP walk data for reference.
(CID:141264840)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 06:10 PM . Last Modified: 2024-04-03 03:05 AM
Dear Shinya Matsuda,
In this case, it would be very correct to make Request modification on the DDF resource:
With respect.
(CID:141264907)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 06:10 PM . Last Modified: 2024-04-03 03:05 AM
Dear Shinya Matsuda,
In this case, it would be very correct to make Request modification on the DDF resource:
With respect.
(CID:141264907)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 06:10 PM . Last Modified: 2024-04-03 03:05 AM
Okay! Thank you for your prompt support.
(CID:141264919)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 06:10 PM . Last Modified: 2024-04-03 03:05 AM
Ok, very thanks for the good feedback 😀.
(CID:141264924)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-05 06:10 PM . Last Modified: 2023-10-22 03:05 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.