Min. Distance Between NetBotz USB Coordinators

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Min. Distance Between NetBotz USB Coordinators
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
aashraf
Lieutenant JG aashraf Lieutenant JG
Lieutenant JG

Posted: ‎2022-01-10 10:00 AM

0 Likes
1
902
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-01-10 10:00 AM

Min. Distance Between NetBotz USB Coordinators

Dears,

 

In one of our projects, We have 30 NetBotz-250 with 25 wireless Temp/RH sensors configured per each NetBotz.
The customer installed each 10 NetBotz in one rack.

 

We have a repeated issue of sensors inactivity on DCE, Specially for the sensors which are far from the NetBotz (But still within 50 ft).


Based on the below attached screenshot the min. recommended distance between wireless devices is 2 ft (60 cm).
So, I'm asking about the min. recommended distance between the coordinators which are directly connected to the NetBotz USB port.

 

Install the wireless temp. sensor.JPG

Labels
  • Labels:
  • Data Center Expert
  • NetBotz
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Reply 1
ATrabert
Lt. Commander ATrabert Lt. Commander
Lt. Commander

Posted: ‎2022-01-11 07:30 AM . Last Modified: ‎2022-01-11 07:31 AM

0 Likes
0
883
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2022-01-11 07:30 AM . Last Modified: ‎2022-01-11 07:31 AM

ideally in a mesh network, the netbot 250/usb coordinator should be in the center of its specific wireless sensors.  I would highly recommend the customer redistribute all of the netbotz 250 so they are distributed evenly throughout the data center.  This will improve communication and prevent excessive battery wear on the sensors closest to the units.

 

Also make sure the coordinator and wireless sensors are running the latest firmware.  They can be updated using this utility

https://www.apc.com/shop/us/en/products//P-SFNBWUTIL101 

 

I realize i didn't answer your specific question, but in my opinion the initial configuration of having all 10 netbotz in the same rack goes against wireless mesh best practices and should be avoided in the first place.  If they correct this, they should see improved wireless sensor communication. 

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of