Launch of Consumer/Home Owner registration process! We are pleased to announce the commencement of the Consumer/Home Owner Registration Process on Community. Consumers/Home Owners may now proceed to register by clicking on Login/Register. The process is straightforward and designed to be completed in just a few steps.
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Search in
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 02:05 PM . Last Modified: 2024-04-05 02:44 AM
Hi,
Running on DCE 7.4.3 and just added this UPS to DCE. Got the required port opened to be able to transfer between DCE and the UPS with right config for account on the UPS. Alarm is still there. I read that maybe I would have to upgrade the firmware on the UPS so I did that. It is now at version 6.5.0 which I update through DCE. I even tried to remove the UPS from DCE and add it again but alarm comes back. What is next step to get the alarm resolved?
Thanks
Toby
(CID:128754908)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 02:06 PM . Last Modified: 2024-04-05 02:44 AM
Hi Toby,
If you've not done so already, check out k-base FA177004. It looks like you've already addressed these points but I just want to be sure.
Another thing to try, if you're using SCP, try instead using FTP for this transfer. You can always change it back later but we want to get that file transferred.
Another thing I'd like to see you try is to get the DDF file manually. You can't add it to DCE but I want to see if the file is available on that unit. Open an FTP session to the device and run the command - get ddf.zip do you actually get a file and are there XML files included?Please note that if you run "ls" to look at the directory structure, you will likely not see the ddf.zip file.
Thanks,
Steve
(CID:128754940)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 02:06 PM . Last Modified: 2024-04-05 02:44 AM
Hi,
According to the event log on the UPS the file is being transfered:
02/09/2018 | 09:44:22 | apc | SSH/SCP: File transfer complete. |
02/09/2018 | 09:43:44 | apc | SSH/SCP: File transfer started. |
02/09/2018 | 09:43:44 | apc | SCP CLI user 'apc' logged in from X.X.X.X. |
I was able to download the file and look at it and it does have XML file in it. Right now I cannot use FTP because of firewall but I really think the file is being transferred. Thanks
Toby
(CID:128755075)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 02:06 PM . Last Modified: 2024-04-05 02:44 AM
Hi Toby,
I have seen SSH fail in the past so I will see if I can get in contact with someone that has an MGE 3500 with an AP9631CH and test using SCP. Can you run an SNMPwalk of the device? Can you send over the DDF.zip that you downloaded from it?
Steve.
(CID:128757881)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 02:06 PM . Last Modified: 2024-04-05 02:44 AM
Hi Toby,
Just an update. I got access to an MGE3500 with an AP9631CH running 6.4.6 firmnware. I turned off FTP. I enabled SSH. I created a device file transfer settings entry for this device using SCP. I then went through with the install and I have received no errors about the DDF file (or anything else for that matter). If you've still got an issue, you may want to try to delete and re-add the device.
Steve
(CID:128760487)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 02:06 PM . Last Modified: 2024-04-05 02:44 AM
Below are the files you requested. I tried it as you suggested and it is still alarming for transferring the file. It is Firmware 6.5.0 running on our AP9631CH.
(CID:128760497)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 02:06 PM . Last Modified: 2024-04-05 02:44 AM
Hi Toby,
I upgraded the NMC in the UPS to 6.5.0. As you can see here, I still do not see the issue:
I removed the device and re-added it and still see no issue.
I have FTP server access off and SCP enabled.
I looked at the SNMPwalk you provided and after upgrading my device, I downloaded the DDF.zip file from it so I could make sure they match up as that's how we verify what is downloaded matches what the card believes we should have.
It does match so the DDF.zip and all it's files are the proper ones for this unit.
All I can suggest is trying to delete the device and re-add it. If the error keeps coming back, there would appear to be something blocking the actual download of the file.
(CID:128760511)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-04 02:06 PM . Last Modified: 2023-10-22 02:59 AM