DCE 7.5.0 - Multiple devices have communication lost alarm

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • DCE 7.5.0 - Multiple devices have communication lost alarm
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:04 PM . Last Modified: ‎2024-04-05 02:45 AM

0 Likes
8
1059
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:04 PM . Last Modified: ‎2024-04-05 02:45 AM

DCE 7.5.0 - Multiple devices have communication lost alarm

I just updated to 7.5.0 about 10 days and one day to another multiple APC devices alerted communication lost error:

As you can see the devices are different models, types but not all alerted; some AP8853 are offline but another is online. The same models have the same firmware (6.x.y).

I have other remote site which shows the same problem.

It is definitely  not a network issue because I did the following troubleshooting in DCE web interface:

  • ping was success to communication lost devices
  • traceroute was success to communication lost devices
  • in desktop client I double checked the device scan option which matched with device settings (using SNMPv3)

I also checked in the server log but nothing tells more on the communication lost.

I rebooted the server and all the communication lost devices came back! But after 2-3 hours the devices went offline (at the moment the server uptime is 5 hours)

Anyway the default scan interval is 5 minutes globally.

 

Can you please help me? I have that fearing I will lose more and more devices from monitoring.

(CID:128754698)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 8
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:04 PM . Last Modified: ‎2024-04-05 02:45 AM

0 Likes
2
1059
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:04 PM . Last Modified: ‎2024-04-05 02:45 AM

Hi Mate how many devices monitored ?

what is the config cpu ram hw of your Dce server?

ed

(CID:128754721)

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:04 PM . Last Modified: ‎2024-04-05 02:45 AM

In response to DCIM_Support
0 Likes
0
1059
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:04 PM . Last Modified: ‎2024-04-05 02:45 AM

Hi Mate

Not sure why my comment was down voted but happy to discuss if you or someone else would care to discuss.

Sounds like you've been given good advise re firmware version and SNMP V3.  How are things progressing now?

The only other DCE server perf area that I've had issues with in the past is the IO performance, measured in IOPS.  Poor IO perf can adversely affect DCE performance in larger sites, e.g. 2000+ nodes but this might be an issue at your site.  Although judging by the VM config and the latency and throughput, this isn't the issue.

Regards

Ed

 

 

(CID:128755261)

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:05 PM . Last Modified: ‎2024-04-05 02:45 AM

In response to DCIM_Support
0 Likes
0
1059
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:05 PM . Last Modified: ‎2024-04-05 02:45 AM

Hi Ed,

I did not down voted your answer.

Yes, SNMPv3 and firmware version 6.4.6 caused the problem. However it was pretty strange that these devices worked well more than 2 weeks without any problem.

By the way I read thru the mentioned K-base FA305661 article and I had devices where the following statement was true:

  • Devices being added to a DCE server for the first time which have AOS 6.4.6 loaded are not affected.

And these devices were also alerted communication lost.

Anyway thank you for the quick help and suggestion and I will take care more on firmware versions. But I have bad experiencies with it because some devices (NMC) can be into hung state during the upgrade and only physical reset is solving the problem. I monitoring devices in more than 40 remote sites where remote hand support is not always available.

Regards,

Mate

(CID:128757840)

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:05 PM . Last Modified: ‎2024-04-05 02:44 AM

0 Likes
0
1059
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:05 PM . Last Modified: ‎2024-04-05 02:44 AM

I have 653 monitored physical devices and 89 virtual sensors (total 742 devices)

DCE is running on VMware: 4 vCPU 16GB RAM with 18+255GB HDD. The repository shows 242.3 GB as size and 6.6GB is in use. Here is a screenshot from VMware resources:

(CID:128757845)

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:05 PM . Last Modified: ‎2024-04-05 02:44 AM

0 Likes
0
1059
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:05 PM . Last Modified: ‎2024-04-05 02:44 AM

Dear Mate Fekete,

As you can see the devices are different models, types but not all alerted; some AP8853 are offline but another is online. The same models have the same firmware (6.x.y).

...

...the device scan option which matched with device settings (using SNMPv3).

From your screenshot: what version of the firmware are you using on your UPS and rPDU? To solve the SNMPv3 problem for the UPS, firmware v6.5.0 is required, and for rPDU, firmware v6.5.2 is required.

With respect.

(CID:128754737)

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:05 PM . Last Modified: ‎2024-04-05 02:44 AM

0 Likes
1
1059
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:05 PM . Last Modified: ‎2024-04-05 02:44 AM

Dear Mate Fekete,

I started my answer to you from the firmware versions because v6.4.6 with active use of SNMPv3 should be avoided in every possible way. This has already been discussed many times here on EcoStruxure IT, for example in topic . See Steven Marchetti answer on this issue:

...So the reason it was not added to the DCE firmware catalog is an issue with SNMP version 3. I thought about this after my previous answer but wanted to verify and get the k-base number before saying anything. K-base FA305661 outlines the issue which could cause problems with people using SNMP version 3. So as not to break their systems, it was decided not to add it to the DCE catalog.

Therefore, if the device does not have a firmware higher than v6.4.6, then to solve the problem you need to downgrade the firmware to the recommended version of v6.4.4. This is always possible using a special utility.

If there are more questions, please ask.

With respect.

(CID:128754821)

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:05 PM . Last Modified: ‎2024-04-05 02:44 AM

In response to DCIM_Support
0 Likes
0
1059
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:05 PM . Last Modified: ‎2024-04-05 02:44 AM

Thank you. I updated the firmware and it solved the problem on some devices but not at all. Here is another screenshot:

The latest firmware for AP7822B is the 6.4.6

As you can see it is pretty strange because the PDU with 6.4.4 are working properly but 6.4.6 are failed and not all!

(CID:128757851)

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 02:05 PM . Last Modified: ‎2023-10-22 01:11 AM

0 Likes
0
1059
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 02:05 PM . Last Modified: ‎2023-10-22 01:11 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of