Low superheat warning

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Low superheat warning
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
126
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Start a Topic
Solved
Anonymous user
Not applicable

Posted: ‎2020-11-24 12:37 AM

0 Likes
2
17890
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-24 12:37 AM

Low superheat warning

I have been getting this warning from my ACRD602P unit.

It's an hot aisle POD, this unit is 1 of 2 units in that POD.

Labels
  • Labels:
  • Data Center Expert
  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Valentin_Kozlov
Lieutenant Valentin_Kozlov Lieutenant
Lieutenant

Posted: ‎2020-11-25 03:11 AM

1 Like
0
17864
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-25 03:11 AM

Hi!

 

You need to paid attention to your cooling unit.

 

A low or zero superheat reading indicates that the refrigerant did not pick up enough heat in the evaporator to completely boil into a vapor. Liquid refrigerant drawn into the compressor typically causes slugging, which can damage the compressor valves and/or internal mechanical components.

See Answer In Context

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 2
Valentin_Kozlov
Lieutenant Valentin_Kozlov Lieutenant
Lieutenant

Posted: ‎2020-11-25 03:11 AM

1 Like
0
17865
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-11-25 03:11 AM

Hi!

 

You need to paid attention to your cooling unit.

 

A low or zero superheat reading indicates that the refrigerant did not pick up enough heat in the evaporator to completely boil into a vapor. Liquid refrigerant drawn into the compressor typically causes slugging, which can damage the compressor valves and/or internal mechanical components.

  • Tags:
  • english
Reply

Link copied. Please paste this link to share this article on your social media post.

Billark
Billark
Cadet

Posted: ‎2023-03-05 05:02 AM . Last Modified: ‎2023-03-05 05:07 AM

1 Like
0
15948
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2023-03-05 05:02 AM . Last Modified: ‎2023-03-05 05:07 AM

Low superheat in a refrigeration or air conditioning system can be caused by several factors, including:

Overcharging of refrigerant: When the refrigerant charge in the system is too high, the system will have low superheat. This is because there is an excess of refrigerant in the system, which can cause the refrigerant to evaporate at a lower temperature than normal, resulting in low superheat.

Underfeeding of refrigerant: When the refrigerant is not properly fed to the evaporator, it can cause low superheat. This can happen due to a faulty thermostatic expansion valve, which can limit the amount of refrigerant that is allowed to enter the evaporator, resulting in insufficient cooling and low superheat.

Insufficient airflow over the evaporator: When there is insufficient airflow over the evaporator, it can cause low superheat. This can happen due to a clogged or dirty air filter, a malfunctioning blower motor or fan, or a blocked or damaged ductwork, which can reduce the amount of heat that is transferred from the air to the refrigerant, causing the refrigerant to evaporate at a lower temperature than normal.

Malfunctioning compressor: A malfunctioning compressor can also cause low superheat. This can happen due to a faulty compressor valve, worn or damaged compressor components, or a faulty compressor motor, which can cause the refrigerant to circulate at a lower rate, resulting in insufficient cooling and low superheat.

Incorrectly sized metering device: When the metering device, such as a thermostatic expansion valve or a capillary tube, is incorrectly sized, it can cause low superheat. If the metering device is too small, it can restrict the flow of refrigerant into the evaporator, resulting in insufficient cooling and low superheat. If the metering device is too large, it can allow too much refrigerant to enter the evaporator, resulting in excess cooling and low superheat.

Reply

Link copied. Please paste this link to share this article on your social media post.

Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore