Hello,
we are taking leak Rope detected errr from our customer's netbotz. We controlled but there is no issue at the DC. What can we do in this situation.
We are taking the same error several times in one day.
Alert Description: | The value of 'Leak-rope' (Leak Detected) indicates that a 'Critical' alert has occurred. |
Alert Type: | Value Error |
Severity: | Critical |
Alert Level: | Second Alert Level |
Sensor: | Leak-rope |
Sensor Value: | Leak Detected |
Access information: | |
Pod: | Sensor Pod |
Time Detected: | 15-02-2016 22:36:27 |
Notification Time: | 15-02-2016 22:56:28 |
Threshold Name: | Default |
Action Name: | Primary E-mail Notification |
Alert ID: | nbErrorCond_16BC28B6 |
Version: | V4_4_0_20140827_1358 |
Graph of 'Leak-rope - Sensor Pod' from 15-02-2016 21:36:27 to 15-02-2016 22:56:28
|
(CID:105465672)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 11:46 PM . Last Modified: 2024-04-09 01:06 AM
Hi Barlas,
The leak rope sensor is basically two wires that will report a leak if there is connectivity between the 2 wires. If the leak rope is in a dirty environment, perhaps there is conductivity due to the dirt. Perhaps it is touching metal? Perhaps it is contacting concrete.
Make sure it is not specific to this sensor. If you have another leak rope connected to another NetBotz appliance, switch them out. Does the issue follow the sensor or does the issue stay with the unit? What troubleshooting have you performed?
Steve
(CID:105465674)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 11:46 PM . Last Modified: 2023-10-31 11:20 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of