I'm trying to use the DCO Excel Import function to associate my rpdu's to a room pdu and specific breaker. Is there a cross reference available for the template?
(CID:105465662)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 11:46 PM . Last Modified: 2024-04-09 01:06 AM
Hi Dean,
Unfortunately It is not possible/supported to associate devices via excel import. It's good use might be when importing equipment for the first time, however using that without training wouldn't be recommended.
Kind regards
(CID:105465728)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 11:46 PM . Last Modified: 2024-04-09 01:06 AM
Dean. I'm not aware of specific documentation, however If you download the excel import template from DCO and open the template file you should see a "receptacle" worksheet. That worksheet contains examples which show how to map an excel import entry to a specific floor pdu panel and breaker slot. You should be able to use those entries as a reference for adding a rack pdu and mapping it to a specific floor device, panel and breaker location. I attached a small xls example which shows how to add a pair of rack pdu's to a rack and assign these rack pdu's to an existing floor pdu, panel and breaker. Regards Greg Sterling
DCO75-template - Community.xls
(CID:105465837)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 11:46 PM . Last Modified: 2023-10-31 11:08 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of