We are currently monitoring our Power Logic PMs connected to our EGX300 through a Modbus DDF. Is there an SNMP version?
(CID:111937559)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2020-07-03 01:01 PM . Last Modified: โ2024-04-08 01:45 AM
Manuel,
Please go to:
https://dcimsupport.apc.com/devices
Here you can find DDF files for specific devices such as your Power Logic PMs. You do not pull data about the gateway itself so you do not need a DDF for the EGX300 itself.
Thanks,
Steve
(CID:111937565)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2020-07-03 01:01 PM . Last Modified: โ2024-04-08 01:45 AM
Manuel,
Please go to:
https://dcimsupport.apc.com/devices
Here you can find DDF files for specific devices such as your Power Logic PMs. You do not pull data about the gateway itself so you do not need a DDF for the EGX300 itself.
Thanks,
Steve
(CID:111937565)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: โ2020-07-03 01:01 PM . Last Modified: โ2023-10-22 02:51 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.