Inrow disvovery problem in DCE;

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Inrow disvovery problem in DCE;
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
125
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
Start a Topic
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:25 AM . Last Modified: ‎2024-04-09 12:56 AM

0 Likes
4
673
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:25 AM . Last Modified: ‎2024-04-09 12:56 AM

Inrow disvovery problem in DCE;

Hi,

I have a problem about discovering inrow devices in the DCE. I access these devices via browser. However I entered  IP range of these devices or IP address of specific inrow device, DCE cannot discover these devices by using SNMP v1.

 

I configure Inrow devices on browser, These configurations;

    -Enabling SNMP communication in the access option

    -I entered 0.0.0.0 NMS IP/Host Name in the access control option. Additionally, I try entering DCE IP address in this, but it does not work.

 

Note: Inrow devices are APC and Inrow devices' model name is IR25,

 

 

I attached two screenshoot related to information of inrow devices.

 

Thanks for your helps;

 

 

 

 

 

 

(CID:105466937)

Labels
  • Labels:
  • Data Center Expert
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:25 AM . Last Modified: ‎2024-04-09 12:56 AM

0 Likes
0
673
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:25 AM . Last Modified: ‎2024-04-09 12:56 AM

Hi Umut,

 

K-base FA226273 may help you walk through SNMP configuration and troubleshooting to get these 2 systems to communicate. 

 

There should be no reason I'm aware of for this unit not to discover especially with the firmware revision you're running. I would verify that you can pull any info from the device using SNMP, potentially with another SNMP utility, there are plenty of free ones out there. Please verify what version of DCE you're running. Also check to see what DDF files you have on your system. I have DCE 7.3.1 and as you can see here, I have the DDF onboard for the device:

 

Steve

(CID:105467020)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:25 AM . Last Modified: ‎2024-04-09 12:56 AM

0 Likes
1
673
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:25 AM . Last Modified: ‎2024-04-09 12:56 AM

I would suggest double checking that you have the SNMP community strings are matching between what is on the InRow device(s) and the SNMP discovery setting on the DCE.    Also make sure that ports 161 & 162 traffic is not blocked by a firewall rule.  Lastly make sure the device is pingable (if it is not then DCE will not even try to communicate with it.  btw Ping is a ICMP protocol so make sure that is not blocked by firewall or dropped on any network switches between the DCE and the Device.

(CID:105467028)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:25 AM . Last Modified: ‎2024-04-09 12:56 AM

In response to DCIM_Support
0 Likes
0
673
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:25 AM . Last Modified: ‎2024-04-09 12:56 AM

Thanks for your answer , Michael When I tried ping to inrow devices, devices were pingable. Additionally, I check DCE discovery setting and inrows device snmp setting. These settings are equal with each other.

(CID:105467036)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-03 12:25 AM . Last Modified: ‎2023-10-31 11:09 PM

0 Likes
0
673
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-03 12:25 AM . Last Modified: ‎2023-10-31 11:09 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore