ITO Discovery and Operations Connection Problem

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • ITO Discovery and Operations Connection Problem
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
109
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
62
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:24 PM . Last Modified: ‎2024-04-09 01:58 AM

0 Likes
9
1178
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:24 PM . Last Modified: ‎2024-04-09 01:58 AM

ITO Discovery and Operations Connection Problem

Hello,

We have run a discovery in ITO and discovered around 120 devices on Operations. After 10-15 minutes we keep losing the connection to the ITO server and get the error as you may see on the screenshot. We can not work on Operaitons because we keep getting the same error. You may find the log files for ITO and operations at the links below. I think that because of too many devices were discovered, ITO server is not working properly. Can you please advice on how to proceed? 

Thanks in advance 

 

2015-12-03--03-07-23_Operations_Logs.7z.log_ITO_Logs.zip

(CID:105457315)

Labels
  • Labels:
  • Data Center Operation
  • Tags:
  • IT Optimize
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:25 PM . Last Modified: ‎2024-04-09 01:58 AM

0 Likes
1
1177
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:25 PM . Last Modified: ‎2024-04-09 01:58 AM

Hello Kaan

During the polling cycles it appears ITO is attempting to poll a large number of VMware guests at which time the polling is exhausting its reserved memory space. To resolve this issue we'd like to you change a configuration parameter on the ITO server which will decrease the amount of reserved memory used by the poller when it executed.

 

Here's a procedure to change the number of assets ITO will attempt to simultaneously poll. This procedure will cause the poller to consume less memory. The amount of time ITO takes to complete polling of all your assets may increase.

* Logon to the IT Optimize server as an administrator user.

* Change to the IT Optimize installation folder. By default this would be: C:\Program Files\SchneiderElectric\ITOptimize\, but this destination folder can be changed during installation, so change to the proper location.

* In the "bin" sub-folder (so the full path would be C:\Program Files\SchneiderElectric\ITOptimize\bin), you'll find a file called "EnergyCenter.ini".

* Edit the EnergyCenter.ini file. The top set of lines in this file will look like this. There are more lines, I'm only showing the top of the file.

service.class=com.viridity.dcos.server.ViridityServer
service.id=EnergyCenter
service.name=Schneider Electric EnergyCenter
service.description=Data Center Energy Management Software
service.startup=auto
service.controls=stop|shutdown

process.priority=high
single.instance=process

working.directory=C:\PROGRA~1\SCHNEI~1\ITOPTI~1

vm.location=java\bin\server\jvm.dll
vm.version.min=1.6
vm.version.max=1.6
vmarg.1=-Xms128m
vmarg.2=-Xmx1024m
vmarg.3=-server
vmarg.4=-Djava.library.path=lib
vmarg.5=-Dviridity.dcos.home=C:\PROGRA~1\SCHNEI~1\ITOPTI~1
vmarg.6=-Dcom.sun.management.jmxremote.port=3333
vmarg.7=-Dcom.sun.management.jmxremote.ssl=false
vmarg.8=-Dcom.sun.management.jmxremote.authenticate=false
vmarg.9=-XX:+HeapDumpOnOutOfMemoryError
vmarg.10=-XX:MaxPermSize=256m
vmarg.11=-Xrs

Immediately after the line "vmarg.11=Xrs", add this line:

vmarg.12=-Dviridity.threadpool.poller.size=15

Save the file, and restart the IT Optimize service.

To restart the service:

* Open the windows services control panel

* Right click on "Schneider Electric EnergyCenter" service choose restart. Only the "EnergyCenter" service needs to be restarted, the "EnergyCenter Database" service does not need to be restarted.

 

Please let us know if the problem is then resolved.

Regards

Greg Sterling

(CID:105457922)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 9
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:24 PM . Last Modified: ‎2024-04-09 01:58 AM

0 Likes
0
1177
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:24 PM . Last Modified: ‎2024-04-09 01:58 AM

Hi Kaan,

Would you mind to share your ITO server hardware specs such as RAM size? and the number of the discovered devices?

According to the ITO logs it seems the server is experiencing out of memory exception and then apparently shutting down, and therefore you are seeing the communication error on DCO.

Kind regards

(CID:105457324)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:24 PM . Last Modified: ‎2024-04-09 01:58 AM

0 Likes
4
1177
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:24 PM . Last Modified: ‎2024-04-09 01:58 AM

Hello Kaan.

 

If you logon to your IT Optmize server, and change to the IT Optimize installation folder (default is C:\Program Files\SchneiderElectric\ITOptimize), do you see any files which have an extension .hprof (the filename is probably something like java_pidxxxx.hprof)?

If yes, can you send us the file? Its probably very large, i.e. 1GB+ in size.

The hprof file contains the details of the ITO process which ran out of memory. We can better analyze the cause of the problem and identify a solution.

 

Regards

 

Greg Sterling

(CID:105457368)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:24 PM . Last Modified: ‎2024-04-09 01:58 AM

In response to DCIM_Support
0 Likes
0
1177
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:24 PM . Last Modified: ‎2024-04-09 01:58 AM

Hello,

Jef Faridi I have checked the specs. We have more then enough according to requirements. 4 CPUs and 16 GB memory. The discovered devices were 126. 

Greg Sterling you may find the link for the log files at the link below. it is around 180 MB. Please look into it and let me know if you need more information.

Thanks. 

http://we.tl/WVsh6DJhbJ

java_pid4476.zip 

(CID:105457757)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:25 PM . Last Modified: ‎2024-04-09 01:58 AM

In response to DCIM_Support
0 Likes
0
1177
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:25 PM . Last Modified: ‎2024-04-09 01:58 AM

Thank you for the hprof file. I'm downloading it and will pass it along to the local engineering team for review. Regards Greg Sterling

(CID:105457801)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:25 PM . Last Modified: ‎2024-04-09 01:58 AM

In response to DCIM_Support
0 Likes
0
1177
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:25 PM . Last Modified: ‎2024-04-09 01:58 AM

Engineering has started reviewing the hprof file. I will update you when we get results. Regards Greg Sterling

(CID:105457821)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:25 PM . Last Modified: ‎2024-04-09 01:58 AM

In response to DCIM_Support
0 Likes
0
1177
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:25 PM . Last Modified: ‎2024-04-09 01:58 AM

Hi Kaan ( Kaan Kutlug ) Just a quick question, while Greg and the team is investigating the data, You have kindly shared the server spec's being 4 cpu's and 16GB of memory. Is this the DCO server specs? If yes, could you please also share the ITO server specs, thanks. Kind regards

(CID:105457894)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:25 PM . Last Modified: ‎2024-04-09 01:58 AM

0 Likes
1
1178
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:25 PM . Last Modified: ‎2024-04-09 01:58 AM

Hello Kaan

During the polling cycles it appears ITO is attempting to poll a large number of VMware guests at which time the polling is exhausting its reserved memory space. To resolve this issue we'd like to you change a configuration parameter on the ITO server which will decrease the amount of reserved memory used by the poller when it executed.

 

Here's a procedure to change the number of assets ITO will attempt to simultaneously poll. This procedure will cause the poller to consume less memory. The amount of time ITO takes to complete polling of all your assets may increase.

* Logon to the IT Optimize server as an administrator user.

* Change to the IT Optimize installation folder. By default this would be: C:\Program Files\SchneiderElectric\ITOptimize\, but this destination folder can be changed during installation, so change to the proper location.

* In the "bin" sub-folder (so the full path would be C:\Program Files\SchneiderElectric\ITOptimize\bin), you'll find a file called "EnergyCenter.ini".

* Edit the EnergyCenter.ini file. The top set of lines in this file will look like this. There are more lines, I'm only showing the top of the file.

service.class=com.viridity.dcos.server.ViridityServer
service.id=EnergyCenter
service.name=Schneider Electric EnergyCenter
service.description=Data Center Energy Management Software
service.startup=auto
service.controls=stop|shutdown

process.priority=high
single.instance=process

working.directory=C:\PROGRA~1\SCHNEI~1\ITOPTI~1

vm.location=java\bin\server\jvm.dll
vm.version.min=1.6
vm.version.max=1.6
vmarg.1=-Xms128m
vmarg.2=-Xmx1024m
vmarg.3=-server
vmarg.4=-Djava.library.path=lib
vmarg.5=-Dviridity.dcos.home=C:\PROGRA~1\SCHNEI~1\ITOPTI~1
vmarg.6=-Dcom.sun.management.jmxremote.port=3333
vmarg.7=-Dcom.sun.management.jmxremote.ssl=false
vmarg.8=-Dcom.sun.management.jmxremote.authenticate=false
vmarg.9=-XX:+HeapDumpOnOutOfMemoryError
vmarg.10=-XX:MaxPermSize=256m
vmarg.11=-Xrs

Immediately after the line "vmarg.11=Xrs", add this line:

vmarg.12=-Dviridity.threadpool.poller.size=15

Save the file, and restart the IT Optimize service.

To restart the service:

* Open the windows services control panel

* Right click on "Schneider Electric EnergyCenter" service choose restart. Only the "EnergyCenter" service needs to be restarted, the "EnergyCenter Database" service does not need to be restarted.

 

Please let us know if the problem is then resolved.

Regards

Greg Sterling

(CID:105457922)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:25 PM . Last Modified: ‎2024-04-09 01:58 AM

In response to DCIM_Support
0 Likes
0
1177
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:25 PM . Last Modified: ‎2024-04-09 01:58 AM

Hello Greg, we have followed the steps above and now everything works fine. Thanks for your support. Kind regards, Kaan Kutlug

(CID:105459055)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:25 PM . Last Modified: ‎2023-10-31 11:19 PM

0 Likes
0
1177
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:25 PM . Last Modified: ‎2023-10-31 11:19 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of