Is there any off the shelf capability to have SBO push data centre grey space asset information to DCO? Pumps, chillers, gennies? Please provide details. If not, we will explore developing this via DCO ETL Import DB
(CID:105457400)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 06:25 PM . Last Modified: 2024-04-09 01:58 AM
Hi Ed,
To my knowledge is there no off the shelf solution for having SBO push data to DCO.
You will need to explore other possibilities.
Thank
Jesper
(CID:105457402)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 06:25 PM . Last Modified: 2024-04-09 01:58 AM
Hi Ed,
To my knowledge is there no off the shelf solution for having SBO push data to DCO.
You will need to explore other possibilities.
Thank
Jesper
(CID:105457402)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 06:25 PM . Last Modified: 2024-04-09 01:58 AM
Thank you
(CID:105457405)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 06:26 PM . Last Modified: 2024-04-09 01:58 AM
Jesper is right - no direct communication between SBO and DCO possible right now. However, SBO can feed Modbus data into DCE which in turn pushes data to DCO. There is a catch here however, SBO can expose only 1 Modbus slave address and hence DCE will see SBO as one modbus device. You can group underlying devices together in DCE.
(CID:105457472)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 06:26 PM . Last Modified: 2024-04-09 01:58 AM
Hi Ajay, we have tried a different route where we use Automation server directly with DCE in place of SBO which pretty much does all the work required via SBO and more cost effective...
(CID:105457506)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 06:26 PM . Last Modified: 2024-04-09 01:58 AM
Thanks Vineet! That works too..either individual ASes or one consolidated ES can feed data into DCE.
(CID:105457573)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 06:26 PM . Last Modified: 2024-04-09 01:58 AM
Check my thread here :https://dcimsupport.apc.com/questions/105459285/integrating-bacnet-devices-to-sxw-dce
(CID:105472064)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-02 06:26 PM . Last Modified: 2023-10-31 11:34 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.