ISX Central Enterprise server message: BBU battery

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • ISX Central Enterprise server message: BBU battery
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:05 AM . Last Modified: ‎2024-04-10 01:19 AM

0 Likes
3
745
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:05 AM . Last Modified: ‎2024-04-10 01:19 AM

ISX Central Enterprise server message: BBU battery

Tengo el siguiente mensaje en un servidor físico de ISX Central (Struxureware Expert):
[ English - I have the following message on a physical server ISX Central (StruxureWare Expert): ]

Información diagnóstica: 
OK:BBU Current Cache Policy value is WriteBack. 
WARNING:Replace BBU battery. Full charge capacity is low. 
INFO:BBU battery capacity is -0,06% (Full Charge is -1 of the 1800 mAh Design Rating). 
INFO:BBU calibration was last performed Fri 09/12/2014 02:24:01 CST and is next scheduled for Thu 12/11/2014 02:24:01 CST based on RAID clock current reading of 10/09/2014 23:54:31

 

(CID:92537141)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:05 AM . Last Modified: ‎2024-04-10 01:19 AM

0 Likes
1
744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:05 AM . Last Modified: ‎2024-04-10 01:19 AM

Hi Angel,

 

Can you advise what version of DCE are you running? The error is reporting the capacity as a negative value which is not accurate. I believe this was an issue that was reported prior to DCE v7.2. 

If you are on an older version, is it possible for you to upgrade to DCE 7.2 or higher? If you have a software support contract, you can request the upgrade link from your local tech support. The RAID battery diagnostic should being to report correctly after the upgrade. 

If however, you are on DCE V7.2 or higher, if may indicate that the RAID battery is degraded to the state of being disabled, which can cause potential performance issues. In this case, the RAID battery may need replacing. If the server is under DELL warranty, they should be able to send you a replacement battery. If the server is under our hardware warranty, local tech support should be able to help out with sending a RAID battery. 

Also, please keep in mind that the system will run a RAID battery test is done every 90 days and you may see messages in the log about the RAID battery when its just testing.

 

Regards,

Breda

(CID:92537219)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
Replies 3
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:05 AM . Last Modified: ‎2024-04-10 01:19 AM

0 Likes
1
745
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:05 AM . Last Modified: ‎2024-04-10 01:19 AM

Hi Angel,

 

Can you advise what version of DCE are you running? The error is reporting the capacity as a negative value which is not accurate. I believe this was an issue that was reported prior to DCE v7.2. 

If you are on an older version, is it possible for you to upgrade to DCE 7.2 or higher? If you have a software support contract, you can request the upgrade link from your local tech support. The RAID battery diagnostic should being to report correctly after the upgrade. 

If however, you are on DCE V7.2 or higher, if may indicate that the RAID battery is degraded to the state of being disabled, which can cause potential performance issues. In this case, the RAID battery may need replacing. If the server is under DELL warranty, they should be able to send you a replacement battery. If the server is under our hardware warranty, local tech support should be able to help out with sending a RAID battery. 

Also, please keep in mind that the system will run a RAID battery test is done every 90 days and you may see messages in the log about the RAID battery when its just testing.

 

Regards,

Breda

(CID:92537219)

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:05 AM . Last Modified: ‎2024-04-10 01:19 AM

In response to DCIM_Support
0 Likes
0
744
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:05 AM . Last Modified: ‎2024-04-10 01:19 AM

Thank you Breda DCE version is 7.2, we had replace the battery (a clock Battery) which in inside the server, then we must to know that later there serve lost the time configuration but is ver simple to retire them via console. Server si running again without issues!!!! Thank You!!!

(CID:92537290)

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:05 AM . Last Modified: ‎2023-10-31 11:18 PM

0 Likes
0
742
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:05 AM . Last Modified: ‎2023-10-31 11:18 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

Contact Support
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of