Power panels with 230V voltage output?

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Power panels with 230V voltage output?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:04 AM . Last Modified: ‎2024-04-10 01:19 AM

0 Likes
4
728
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:04 AM . Last Modified: ‎2024-04-10 01:19 AM

Power panels with 230V voltage output?

Hello everybody.

I finding some issues to get the proper power values in a power path that I set up on DCO 7.4.

 

I'm trying to connect a power panel (input : 104A, 400V, 50hz, 3phase) with an APC rackPDU (model AP8653, using a generic one because the genome doesn't come in the library) that distributes one phase power to the loads in the rack (230V). The rack pdu is conected to the power panel using a 32A L1-L2 phase breaker.

 

I can't find the proper values in the power panel to select a power output voltage of 230v/50hz, the only values are for three phase.

 

 

Using a 400V voltage output for the power panel I'm getting wrong capacity values in the rack (it shows 10kW when should be around 6 kW). The output voltage value is set in 230v, 50hz, one phase.

 

 

I don't know if I am missing something between the two elements (power panel and rPDU) or if I did something wrong.

 

Thanks.

(CID:92536958)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:04 AM . Last Modified: ‎2024-04-10 01:19 AM

0 Likes
0
728
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:04 AM . Last Modified: ‎2024-04-10 01:19 AM

Hi Manuel,

You are on the right track. You have set the right input voltage on the Power Panel namely 3PH 400V/50Hz. Also the voltage for the rPDU is correctly set to 230V/50Hz. The result you are seeing is due to the fact that you have connected a 2 phase line-to-line breaker between the power panel and the rPDU. You need to connect a single phase breaker.

If you have a Line-to-Line breaker, the value you will see will equal 0.8 * 32A * sqrt (3) * 1 * 230v which is approximately 10kW. 

If you have a Line-to-neutral breaker, the watts you will see will equal 0.8 * 32A * 3 *1 *230v which equals approximately 6kW.

(Operation is using a power factor of 1 and a derating of 0.8 - the latter can be set in the preferences)

In your example it implies that you need to use a single phase 32A Breaker connected to e.g. L1

Best Regards

    Anders

PS. AP8653 is included in the next release of DC Operation.

(CID:92536995)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 4
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:04 AM . Last Modified: ‎2024-04-10 01:19 AM

0 Likes
0
729
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:04 AM . Last Modified: ‎2024-04-10 01:19 AM

Hi Manuel,

You are on the right track. You have set the right input voltage on the Power Panel namely 3PH 400V/50Hz. Also the voltage for the rPDU is correctly set to 230V/50Hz. The result you are seeing is due to the fact that you have connected a 2 phase line-to-line breaker between the power panel and the rPDU. You need to connect a single phase breaker.

If you have a Line-to-Line breaker, the value you will see will equal 0.8 * 32A * sqrt (3) * 1 * 230v which is approximately 10kW. 

If you have a Line-to-neutral breaker, the watts you will see will equal 0.8 * 32A * 3 *1 *230v which equals approximately 6kW.

(Operation is using a power factor of 1 and a derating of 0.8 - the latter can be set in the preferences)

In your example it implies that you need to use a single phase 32A Breaker connected to e.g. L1

Best Regards

    Anders

PS. AP8653 is included in the next release of DC Operation.

(CID:92536995)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:05 AM . Last Modified: ‎2024-04-10 01:19 AM

0 Likes
1
728
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:05 AM . Last Modified: ‎2024-04-10 01:19 AM

Thanks so much it worked!

I was using the wrong breaker. I changed it and know the capacity values are correct.

 

Maths always tell the truth.....😀

(CID:92537075)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:05 AM . Last Modified: ‎2024-04-10 01:19 AM

In response to DCIM_Support
0 Likes
0
728
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:05 AM . Last Modified: ‎2024-04-10 01:19 AM

I'm glad you got your problem solved :-)

(CID:92537092)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 09:05 AM . Last Modified: ‎2023-10-31 11:30 PM

0 Likes
0
728
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 09:05 AM . Last Modified: ‎2023-10-31 11:30 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of