I need support to configure a SWO cooling system in my customer

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • I need support to configure a SWO cooling system in my customer
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
111
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:15 PM . Last Modified: ‎2024-04-09 02:02 AM

0 Likes
9
705
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:15 PM . Last Modified: ‎2024-04-09 02:02 AM

I need support to configure a SWO cooling system in my customer

Hello, my customer has a DC room with downflow CRACs in other room and I haven't could to set the SWO cooling system well. Can I upload a SWO backup in order to anybody check it?

Regards,

 

Enric

(CID:105456917)

Labels
  • Labels:
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 9
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:15 PM . Last Modified: ‎2024-04-09 02:02 AM

0 Likes
0
704
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:15 PM . Last Modified: ‎2024-04-09 02:02 AM

Can you send in some snapshots and more detail so that we can look into?

(CID:105456961)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:15 PM . Last Modified: ‎2024-04-09 02:02 AM

0 Likes
0
704
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:15 PM . Last Modified: ‎2024-04-09 02:02 AM

Hello Enric, Please provide backups and an exact description of this issue. Thanks Victor

(CID:105456998)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:15 PM . Last Modified: ‎2024-04-09 02:02 AM

0 Likes
0
704
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:15 PM . Last Modified: ‎2024-04-09 02:02 AM

Hi Enric Climent, did you see this? Best, Stine

(CID:105457334)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:15 PM . Last Modified: ‎2024-04-09 02:02 AM

0 Likes
1
704
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:15 PM . Last Modified: ‎2024-04-09 02:02 AM

Hello,

The problem is in the room called "Sala CPD1". I've put the CRACs in the same room with a separate wall, as it's in real. 

Regards,

Enric

(CID:105457604)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:15 PM . Last Modified: ‎2024-04-09 02:02 AM

In response to DCIM_Support
0 Likes
0
704
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:15 PM . Last Modified: ‎2024-04-09 02:02 AM

Hi Enric, I will look into this and get back to you soon, thanks. Kind regards

(CID:105457664)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:16 PM . Last Modified: ‎2024-04-09 02:01 AM

0 Likes
0
704
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:16 PM . Last Modified: ‎2024-04-09 02:01 AM

Hi Enric,

I think the following hints would help you to configure the Downflow CRACs placed outside of the room.

Configure the room to support "Drop ceiling" (and Drop ceiling height)

Right-click on floor > Properties > Ceiling > Drop ceiling . "Yes"

 

Downflow CRACs with ducts to ceiling

Right-click on equipment/downflow CRAC > Properties > Cooling > enable "Duct to ceiling"

Your "Vertical grilles" seems to be fine, but at least one "Perforated Ceiling Tile" would be needed,

 

Hope this helps,

Kind regards

(CID:105457688)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:16 PM . Last Modified: ‎2024-04-09 02:01 AM

0 Likes
1
704
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:16 PM . Last Modified: ‎2024-04-09 02:01 AM

 

Hi Jef,

Thanks for your hints. Now it seems running better but there are some errors as follow

How can I solve this problem?

Regards,

 

Enric

 

(CID:105457711)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:16 PM . Last Modified: ‎2024-04-09 02:01 AM

In response to DCIM_Support
0 Likes
0
704
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:16 PM . Last Modified: ‎2024-04-09 02:01 AM

Hello Enric, I see a few issues that are causing the errors that you may be seeing. Please see below, Cracs have been configured for 1.5kw of cooling which appears to be very low. We are mix cooling models by using downflow and vertical vents. The vertical vents are not exhausting any hot air from the data center because the properties of the vertical vents are set to zero cfm. With this configuration, when adding airflow properties with a vertical vent will create an air flow imbalance that we can not correct. Here is my recommendation: add a drop ceiling, place ceiling tiles in the same location as the vertical vents and lastly duct the cooling units to the ceiling. Please let me know if you have any questions. Thanks Victor

(CID:105457760)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 06:16 PM . Last Modified: ‎2023-10-31 11:09 PM

0 Likes
0
704
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 06:16 PM . Last Modified: ‎2023-10-31 11:09 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of