I am testing Tripp-Lite UPS unit compatibility with Struxureware software and found that Struxureware is not able to report any information, critical alarms from Tripp-Lite UPS unit in short or details email alert.

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forĀ 
ShowĀ Ā onlyĀ  | Search instead forĀ 
Did you mean:Ā 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • I am testing Tripp-Lite UPS unit compatibility with Struxureware software and found that Struxureware is not able to report a...
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
108
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
62
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ā€Ž2020-07-04 08:05 PM . Last Modified: ā€Ž2024-04-04 04:20 AM

0 Likes
12
2276
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ā€Ž2020-07-04 08:05 PM . Last Modified: ā€Ž2024-04-04 04:20 AM

I am testing Tripp-Lite UPS unit compatibility with Struxureware software and found that Struxureware is not able to report any information, critical alarms from Tripp-Lite UPS unit in short or details email alert.

Hi 

I am testing Tripp-Lite UPS unit compatibility with Struxureware software and found that Struxureware is not able to report any information, critical alarms from Tripp-Lite UPS unit in short or details email alert. All i can get is communication lost alert when device looses connection to the Struxureware software. 

I added the units using SNMP and then installed the DDF associated to Tripp-Lite web card – WEBCARDLX from http://sxwhelpcenter.ecostruxureit.com/  Website. I can view the device sensors which is a good sign of device being able to communicate with Struxureware software.

Under the alarm configuration tab I can see ā€œUPS On Batteryā€ alarm sensor for the Tripp-Lite units as well.

All the information getting displayed for Tripp-Lite is same as other APC units we are testing under Struxureware but for some reason I am not getting the email alarm’s from Tripp-Lite units.

I am not sure if we need to get the correct DDF file created from DCIM support as Tech support guys advised to post question to the DCIM support to look into this matter. 

 

GP 

(CID:132663735)

Labels
  • Labels:
  • Data Center Expert
  • Tags:
  • bug
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 12
DCIM_Support
Picard DCIM_Support
Picard

Posted: ā€Ž2020-07-04 08:05 PM . Last Modified: ā€Ž2024-04-04 04:20 AM

0 Likes
1
2275
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ā€Ž2020-07-04 08:05 PM . Last Modified: ā€Ž2024-04-04 04:20 AM

Hi Gagan!

Check that your devices are added to correct notification policy ubder the "Devices" tab.

It is important thing that device alarms ("blue tab") can be linked to one notification policy only. And threshold alarm ("orange tab") can be linked to several policies.

Communication lost alarm is "orange" one and its created automatically when you discover your device.

 

(CID:132663818)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ā€Ž2020-07-04 08:05 PM . Last Modified: ā€Ž2024-04-04 04:20 AM

In response to DCIM_Support
0 Likes
0
2275
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ā€Ž2020-07-04 08:05 PM . Last Modified: ā€Ž2024-04-04 04:20 AM

Hi Valentin 

As you can see in the screen shot the device alarm - UPS Battery discharged, UPS Low battery and UPS On battery are part of default notification policy.

 The default notification policy has all devices listed under it and a Threshold (Communication status and State mismatch - Battery status created by me listed in it). I have only created one alarm action which is Send E-mail alarm action and no other alarm options are present in the DCE client. 

 

 

(CID:132664271)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ā€Ž2020-07-04 08:05 PM . Last Modified: ā€Ž2024-04-04 04:20 AM

0 Likes
0
2275
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ā€Ž2020-07-04 08:05 PM . Last Modified: ā€Ž2024-04-04 04:20 AM

Dear Gagan,

From your question:

I added the units using SNMP and then installed the DDF associated to Tripp-Lite web card – WEBCARDLX from http://sxwhelpcenter.ecostruxureit.com/  Website.

Tell us, please, what version is your SNMP DDF-file for WEBCARDLX? Also, please tell us which model of your Tripp Lite UPS? This information is important.

Under the alarm configuration tab I can see ā€œUPS On Batteryā€ alarm sensor for the Tripp-Lite units as well.

You mean the alarm configuration tab in DCE software? Please show a screenshot of this.

The fact is that today, from the web-resource Device Support, I was able to download the SNMP DDF-file for WEBCARDLX tripplite_webcardlx.xml: its version 2. And in this DDF-file there are only three configured Device Alarms:

Tlp Env Temperature In Alarm Condition Present/Cleared (warning)
Tlp Env Humidity In Alarm Condition Present/Cleared (warning)
Tlp Env Input Contact In Alarm Condition Present/Cleared (warning)

I did not find in this DDF-file specified by you "UPS On Battery" alarm sensor...

With respect.

(CID:132663832)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ā€Ž2020-07-04 08:05 PM . Last Modified: ā€Ž2024-04-04 04:19 AM

0 Likes
0
2275
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ā€Ž2020-07-04 08:05 PM . Last Modified: ā€Ž2024-04-04 04:19 AM

  1. Tell us, please, what version is your SNMP DDF-file for WEBCARDLX? Also, please tell us which model of your Tripp Lite UPS? This information is important.

 

    TrippLite WEBCARDLX - Verison 2 
    Model of Tripp Lite UPS used - SU750RTXLCD2U & SU1500RTXLCD2U
    In addition I also installed DDF for Tripp Lite UPS - Version 6

 

      2.

Alarm configuration tab

    in DCE software. Please show a screenshot of this.


    I hope all these screen shots will answer your question. 

 

    As I stated in my question. For the Tripp Lite units I can get details under Device Alarm Configuration TAB for UPS Battery Discharged (Severity - Warning , Enabled - Yes). UPS on Battery (Severity - Critical, Enabled  - yes ). My understanding is that I should also get alarm notification for these options.
    Example - IF there is a power loss and UPS is no longer on Utility power, we should receive an alarm notification (Severity - Critical) with UPS On Battery alert.
    I spoke with Tripp Lite support and they told me that Tripp Lite units uses Port 161 and 162 for sending and listening to SNMP traps. 
    SNMP walk query send over port 161 and listen to device on Port 162. 
    Can this be our issue of not able to get alerts from Tripp Lite UPS ??

 

    GP



 

(CID:132664228)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ā€Ž2020-07-04 08:05 PM . Last Modified: ā€Ž2024-04-04 04:19 AM

0 Likes
0
2275
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ā€Ž2020-07-04 08:05 PM . Last Modified: ā€Ž2024-04-04 04:19 AM

Did you check your notification policy?

Are there your devices under "Device" tab?

(CID:132664276)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ā€Ž2020-07-04 08:06 PM . Last Modified: ā€Ž2024-04-04 04:19 AM

0 Likes
0
2275
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ā€Ž2020-07-04 08:06 PM . Last Modified: ā€Ž2024-04-04 04:19 AM

Also, if you have UPS State sensor or similar, you can create state treshold and receive alerts this way.

(CID:132664278)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ā€Ž2020-07-04 08:06 PM . Last Modified: ā€Ž2024-04-04 04:19 AM

0 Likes
0
2275
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ā€Ž2020-07-04 08:06 PM . Last Modified: ā€Ž2024-04-04 04:19 AM

Hi Valentin 

Yes we see the devices under the Default -> Notification policy -> Devices TAB. 

 

Threshold - I created a State Mismatch Threshold for Battery Status. 

Threshold is also linked to Default Notification Policy and Default notification has only one alarm Test123 created no other duplicate present under it. 

As per the Threshold policy created we should get an alarm when Battery gets discharged after power outage. But its not happening. 

 

 

(CID:132664317)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ā€Ž2020-07-04 08:06 PM . Last Modified: ā€Ž2024-04-04 04:19 AM

0 Likes
0
2275
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ā€Ž2020-07-04 08:06 PM . Last Modified: ā€Ž2024-04-04 04:19 AM

Dear Gagan,

Thanks for the screenshots and detailed information.

In addition I also installed DDF for Tripp Lite UPS - Version 6

This information was not enough for me to understand in your question šŸ˜€. Now everything is clear to me and everything corresponds to reality.

I spoke with Tripp Lite support and they told me that Tripp Lite units uses Port 161 and 162 for sending and listening to SNMP traps.
SNMP walk query send over port 161 and listen to device on Port 162.
Can this be our issue of not able to get alerts from Tripp Lite UPS ??

This does not matter, since the DCE-server polls the 3rd-party devices on a standard 161 SNMP port and does not accept SNMP traps from them (as opposed to native Schneider Electric devices).

As per the Threshold policy created we should get an alarm when Battery gets discharged after power outage. But its not happening.

I.e., when your UPS is really running on batteries, you do not see a critical alarm in the DCE-client? Do I understand you correctly?

Or a critical alarm, still appears in the DCE-client, but you do not receive an e-mail notification about this?

With respect.

(CID:132664551)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ā€Ž2020-07-04 08:06 PM . Last Modified: ā€Ž2024-04-04 04:19 AM

0 Likes
0
2275
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ā€Ž2020-07-04 08:06 PM . Last Modified: ā€Ž2024-04-04 04:19 AM

Dear Gagan,

Tell us, please, did you solve your problem or not?

With respect.

(CID:132670115)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ā€Ž2020-07-04 08:06 PM . Last Modified: ā€Ž2024-04-04 04:19 AM

0 Likes
0
2275
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ā€Ž2020-07-04 08:06 PM . Last Modified: ā€Ž2024-04-04 04:19 AM

I realize this post is older, but in case anyone else is struggling with the same issue, I thought I'd chime in. Short version: this should be fixed in WEBCARDLX versions 15.5.2 and later. Details on why I believe that to be true are below.

*Note: I work for Tripp Lite support and worked with a customer on a similar issue. I became aware of this thread because other users have seen it and thought the issue still exists. The issue I was working on is what prompted me to post this thread last year: Need a DDF file for the Tripp Lite WEBCARDLX Struxureware v7.2.2*

I believe the root cause of this particular problem was related to an issue with WEBCARDLX firmware versions from 15.04 to 15.5.1. We resolved the issue in firmware 15.5.2.

The issue was: the WEBCARDLX was NOT changing the number reported to " upsAlarmsPresent" nor populating the " upsAlarmTable" when an alarm was present. Since Struxureware polls the UPS MIB, and not UPS vendor-specific MIBs (e.g. in our case  tlpAlarmsPresent) , it was unable to detect the alarms on the WEBCARDLX. This being the root cause is also consistent with spezialist 's point about the SNMP Traps not mattering in this case.

The customer I was working with was able to confirm firmware 15.5.2 resolved their issue. Note: we have since released later firmware that should also work.

Gagan wish I would have saw this sooner. If you are still struggling with this issue, feel free to reach out to me and I can try and help.

(CID:140217160)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ā€Ž2020-07-04 08:06 PM . Last Modified: ā€Ž2024-04-04 04:19 AM

0 Likes
0
2275
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ā€Ž2020-07-04 08:06 PM . Last Modified: ā€Ž2024-04-04 04:19 AM

**Adding my comment above as an "Answer"**

I realize this post is older, but in case anyone else is struggling with the same issue, I thought I'd chime in. Short version: this should be fixed in WEBCARDLX versions 15.5.2 and later. Details on why I believe that to be true are below.

*Note: I work for Tripp Lite support and worked with a customer on a similar issue. I became aware of this thread because other users have seen it and thought the issue still exists. The issue I was working on is what prompted me to post this thread last year: Need a DDF file for the Tripp Lite WEBCARDLX Struxureware v7.2.2*

I believe the root cause of this particular problem was related to an issue with WEBCARDLX firmware versions from 15.04 to 15.5.1. We resolved the issue in firmware 15.5.2.

The issue was: the WEBCARDLX was NOT changing the number reported to " upsAlarmsPresent" nor populating the " upsAlarmTable" when an alarm was present. Since Struxureware polls the UPS MIB, and not UPS vendor-specific MIBs (e.g. in our case  tlpAlarmsPresent) , it was unable to detect the alarms on the WEBCARDLX. This being the root cause is also consistent with spezialist 's point about the SNMP Traps not mattering in this case.

The customer I was working with was able to confirm firmware 15.5.2 resolved their issue. Note: we have since released later firmware that should also work.

Gagan wish I would have saw this sooner. If you are still struggling with this issue, feel free to reach out to me and I can try and help.

(CID:140217193)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ā€Ž2020-07-04 08:06 PM . Last Modified: ā€Ž2023-10-22 02:37 AM

0 Likes
0
2275
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ā€Ž2020-07-04 08:06 PM . Last Modified: ā€Ž2023-10-22 02:37 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings Ā© 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of