EcoStruxure IT forum
Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2020-07-05 07:50 PM . Last Modified: ‎2024-04-03 02:31 AM
Hello,
I am using MIB Browser and have loaded the PowerNet MIB. I managed to get some parameters of the MIB (under the apcmgmt folder), however it does not work for SNMP objects under the products folder (object not found).
I would like to be able to read with SNMP "gets" the status of my sensors (temperature, humidity, doors status open/closed). Could you please help me to do so ?
Thanks
(CID:144314080)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2020-07-05 07:50 PM . Last Modified: ‎2024-04-03 02:30 AM
Hi Laurent,
Before looking for the correct OID, we'd need to know what product you're using and what sensors.
Thanks,
Steve
(CID:144314139)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2020-07-05 07:50 PM . Last Modified: ‎2024-04-03 02:30 AM
Hello Steve
I have the Netbotz 250 (model NBRK0250, HW Rev 05, FW Rev 0.7.6).
The wired sensors are
- door switch : NBES0302
- Temperature and humidity : AP9335TH APC.
Regards
Laurent
(CID:144868354)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2020-07-05 07:50 PM . Last Modified: ‎2024-04-03 02:30 AM
Hello,
By chance I have been able to find the information into the MIB.
The doors sensors status can be fetched in the table : memDoorsSensorsStatusTable.
The temperature / humidity sensor status can be read under : memSensorsStatusTable.
Both are tables so a snmptable command must be used.
Regards
(CID:144868352)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2020-07-05 07:51 PM . Last Modified: ‎2024-04-03 02:30 AM
Thank you for the support
(CID:144868356)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: ‎2020-07-05 07:51 PM . Last Modified: ‎2023-10-22 02:33 AM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.