Hi everyone!
How to model Emerson PCW unit in DCO?
It's a downflow unit, but it stands on legs and flows above raised floor.
There are no perforated tiles in design.
What type of cooling unit I need to use in order to model cooling properly?
(CID:100340554)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-02 03:02 PM . Last Modified: β2024-04-09 03:59 AM
Hello Valentin,
I would recommended using the vertical vent option for this model. The reason I recommend that type of cooling model is because you have the ability to place the supply air at the bottom of the wall and the return above . This would allow the model to better represented. Please see the EcoBreeze section of the video below.
How to model different types of cooling
Thank You
(CID:100340567)
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: β2020-07-02 03:02 PM . Last Modified: β2023-10-31 11:06 PM
This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.