How to compensate for exhaust chimney in DCO

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • How to compensate for exhaust chimney in DCO
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 09:14 PM . Last Modified: ‎2024-04-04 03:50 AM

0 Likes
3
730
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 09:14 PM . Last Modified: ‎2024-04-04 03:50 AM

How to compensate for exhaust chimney in DCO

I have a number of cabinets that have sealed back doors and exhaust chimneys.

These particular exhaust chimneys are powered and metered. They are being monitored in DCE. 

These are "OpenGate" EC30 and Geist "ActiveAir" (OpenGate was acquired by Geist, so it is much the same thing)

 

These units record the return air temperature in the chimney, the CFM, the % load on the chimney fan system, the humidity, external temperature, etc

 

Obviously, DCO needs to have these associated with the cabinets - so that it can properly interpret the information.

 

However, I do not see ANY chimney system in the genome library, unless I am not searching under the wrong key words. As these sit atop the cabinet, and pull air directly out of hte room and into the plenum, the tool must understand the purpose and use of the object for it to be utilized, I can't just create my own object.

These Chimney systems are hardly new. Some of the ones we're using have been in place for more than 5 years, but less than 10.

Can someone point me to the instructions on how to set this up?

 

Thank you

 

(CID:133367670)

Labels
  • Labels:
  • Data Center Expert
  • Data Center Operation
  • Genome
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 3
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 09:14 PM . Last Modified: ‎2024-04-04 03:50 AM

0 Likes
0
729
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 09:14 PM . Last Modified: ‎2024-04-04 03:50 AM

The chimney system is not part of the genome library - it is a setting on the rack itself.

If you select "Duct to ceiling:" in the rack properties, the rack will build a chimney on top of itself.

The chimney is not an object and you will not be able to associate device measurements to the chimney - only to the rack.

From Tips and tricks for configuring cooling:

When using the duct-to-ceiling feature please make sure that you balance the airflow. The amount of airflow coming from the ducted racks should be similar to the amount of airflow to the ducted cooling units. If there is a large unbalance the air will leak in or out from the ceiling. This is handled by the cooling calculator, but the results can be difficult to interpret.

One indication that the calculations encounter an under-pressure in the ducted ceiling is that the Cooling Load on the cooling units is very low.

Good luck!

(CID:133368020)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 09:14 PM . Last Modified: ‎2024-04-04 03:50 AM

0 Likes
0
729
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 09:14 PM . Last Modified: ‎2024-04-04 03:50 AM

Ok, that explains that - but the numbers don't match the calculations shown in the manual  

   1. against name plate

   2. against the real power drawn - which is a known value in DCO

   3. against the real CFM drawn by the chimneys - which is a known value in DCE

How do I associate the exhaust fan? 

   1. these are not new pieces of equipment

   2. DCE has the information

 

Realistically, DCO should be integrated with DCE and pick up the information - It should be a matter of the user deciding to use the DCE objects or not in DCO - just a check box for every item in DCE - we might as well be buying 2 different tools from 2 different companies almost.

(CID:133369476)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-04 09:14 PM . Last Modified: ‎2023-10-22 02:27 AM

0 Likes
0
729
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-04 09:14 PM . Last Modified: ‎2023-10-22 02:27 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of