Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Join our "Ask Me About" community webinar on May 20th at 9 AM CET and 5 PM CET to explore cybersecurity and monitoring for Data Center and edge IT. Learn about market trends, cutting-edge technologies, and best practices from industry experts.
Register and secure your Critical IT infrastructure

Migration of physical machines to virtual machines

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • Migration of physical machines to virtual machines
Options
  • Subscribe to RSS Feed
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
109
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
62
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to EcoStruxure IT forum
Solved
DCIM_Support
Picard DCIM_Support
Picard

Posted: โ€Ž2020-07-04 09:12 PM . Last Modified: โ€Ž2024-04-04 03:51 AM

0 Likes
15
1727
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 09:12 PM . Last Modified: โ€Ž2024-04-04 03:51 AM

Migration of physical machines to virtual machines

Hello

Our client has requested that we migrate from physical machines to virtual machines; the DCO, DCE and OPTIMIZE systems.

Client has provided us with 2 HP PROLIANT DL380 GEN10 servers, 12CPUs x Intel (R) Xeon (R) Gold 6128 CPU at 3.40GHz, total memory of 128 GB, with the same features; in each one of them it is required to install the 3 systems that we administer. On the other hand, other virtual machines with other management systems will be installed on the same servers (3 more systems).

So far, the information of our system is:

DCO Versiรณn 8.2.7, we have 100 Rack and more than 800 devices installed

DCE Versiรณn 7.5.0, we have more than 800 monitored devices

Optimize Versiรณn 7.5.2, we have 100 monitored devices

The query is: What is the best topology and / or architecture that we must manage so that we do not have problems when migrating to virtual machines (Vmware ESXi version 6.5.0)?

I have already developed my table with the appropriate system requirements for migration, after verification of the URLs provided. What I want is to have the certainty that the information is correct before making the migration.

 

Thanks for the help.

 regards

 

Caroll Silva

(CID:132671990)

Labels
  • Labels:
  • Data Center Expert
  • Data Center Operation
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
DCIM_Support
Picard DCIM_Support
Picard

Posted: โ€Ž2020-07-04 09:12 PM . Last Modified: โ€Ž2024-04-04 03:51 AM

0 Likes
10
1726
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 09:12 PM . Last Modified: โ€Ž2024-04-04 03:51 AM

Hi Caroll,

 

Good day!

For the DCE Physical to VM Migration, the best and the recommended way of doing it is to download the DCE VM (AP94VMTRL) purchase the activation license (AP94VMACT) and once the DCE VM has been activated, refer to this link (click here) to apply the corresponding VM configuration based on the hardware server equivalent. You have to at least know the model number of the DCE to confirm this (AP9465 = Basic, AP9470 = Standard, AP9475 = Enterprise)

Once the hardware VM settings are applied, you can then purchase a software support contract based on the appliance and the number of nodes that it manages (I suggest these SKUs: WMS1YRVM + WMS1YR1000N)

Once the DCE software contract has been applied, contact the local support and provide the following information so they can assist you with the node license transfer from the physical to the virtual DCE.

DCO is slightly similar. As soon as a software contract is in place, let the local support team know so they can transfer the existing module licenses from physical to the virtual DCE. The minimum system requirement for DCO (click here) should suffice.

As long as the VM DCO and DCE are deployed on the same network range as their predecessors everything should work out okay.


I hope this answers your question.

 

Kind regards,

 

Justine Chester

(CID:132672078)

See Answer In Context

Reply

Link copied. Please paste this link to share this article on your social media post.

Replies 15
DCIM_Support
Picard DCIM_Support
Picard

Posted: โ€Ž2020-07-04 09:12 PM . Last Modified: โ€Ž2024-04-04 03:51 AM

0 Likes
10
1727
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 09:12 PM . Last Modified: โ€Ž2024-04-04 03:51 AM

Hi Caroll,

 

Good day!

For the DCE Physical to VM Migration, the best and the recommended way of doing it is to download the DCE VM (AP94VMTRL) purchase the activation license (AP94VMACT) and once the DCE VM has been activated, refer to this link (click here) to apply the corresponding VM configuration based on the hardware server equivalent. You have to at least know the model number of the DCE to confirm this (AP9465 = Basic, AP9470 = Standard, AP9475 = Enterprise)

Once the hardware VM settings are applied, you can then purchase a software support contract based on the appliance and the number of nodes that it manages (I suggest these SKUs: WMS1YRVM + WMS1YR1000N)

Once the DCE software contract has been applied, contact the local support and provide the following information so they can assist you with the node license transfer from the physical to the virtual DCE.

DCO is slightly similar. As soon as a software contract is in place, let the local support team know so they can transfer the existing module licenses from physical to the virtual DCE. The minimum system requirement for DCO (click here) should suffice.

As long as the VM DCO and DCE are deployed on the same network range as their predecessors everything should work out okay.


I hope this answers your question.

 

Kind regards,

 

Justine Chester

(CID:132672078)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: โ€Ž2020-07-04 09:12 PM . Last Modified: โ€Ž2024-04-04 03:51 AM

In response to DCIM_Support
0 Likes
0
1726
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 09:12 PM . Last Modified: โ€Ž2024-04-04 03:51 AM

Thanks for the clarifications. I detail the architecture:

2 Physical servers, with the following features each:

HP PROLIANT DL380 GEN10, total memory of 128 GB

- VM DCE: 4 CPU, 4G RAM
- VM DCO: 8 CPU, 32G RAM
- VM IT OPTIMIZE: 4CPU, 4G RAM


DCE: Consultation:
- If expert server 1 fails, how is the information transferred to server 2, is it manual?
- The same licenses are valid for both server 1 and server2?

Note: In DCE We have part number AP9475

We also have the SKU: WMS1YR1000N

Regards

Caroll 

 

(CID:133373018)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: โ€Ž2020-07-04 09:12 PM . Last Modified: โ€Ž2024-04-04 03:51 AM

In response to DCIM_Support
0 Likes
0
1726
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 09:12 PM . Last Modified: โ€Ž2024-04-04 03:51 AM

Dear Caroll Silva,

From your comments:

- If expert server 1 fails, how is the information transferred to server 2, is it manual?

Yes, in the simplest case only in manual mode, for example, through DCE full backup procedure. But you can also automatically, if you use the VMware High Availability (licensed separately by VMware). I.e., you have two ESXi hosts, but all your virtual machines (DCE, DCO, ITO, etc,) will only be in one instance (not as you have drawn above).

In case of any problems or maintenance of the main ESXi host, all your virtual machines just move to the spare ESXi host without interrupting the service and continue to work there.

- The same licenses are valid for both server 1 and server2?

If you mean two separate virtual machines DCE as you have drawn, then no: you will need to buy two separate licenses (licenses are tied to MAC addresses).

With respect.

(CID:133373062)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: โ€Ž2020-07-04 09:12 PM . Last Modified: โ€Ž2024-04-04 03:51 AM

In response to DCIM_Support
0 Likes
0
1726
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 09:12 PM . Last Modified: โ€Ž2024-04-04 03:51 AM

Spot on ๐Ÿ™‚

(CID:133373077)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: โ€Ž2020-07-04 09:12 PM . Last Modified: โ€Ž2024-04-04 03:51 AM

In response to DCIM_Support
0 Likes
0
1726
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 09:12 PM . Last Modified: โ€Ž2024-04-04 03:51 AM

I have another question

we already obtained the DCE virtual license, the DCE backup was restored and the license was added acquired virtual

In DCO your backup was restored and in Optimize your backup was also restored.

Then, the external virtual DCE and virtual Optimize in virtual DCO server were integrated.

All the devices were associated and started with the validations which I describe:

DCE reads all devices correctly
But DCO, can not display the measured data of the r-pdus. Some idea because that happens.

regards

(CID:138810558)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: โ€Ž2020-07-04 09:12 PM . Last Modified: โ€Ž2024-04-04 03:51 AM

In response to DCIM_Support
0 Likes
0
1726
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 09:12 PM . Last Modified: โ€Ž2024-04-04 03:51 AM

Dear Caroll Silva,

From your comments:

...DCE reads all devices correctly
But DCO, can not display the measured data of the r-pdus. Some idea because that happens.

If you use native =SE= rPDUs, then you need a special patch file. This patch is very easy to install (or removed) to the DCE-server, as it is described in the example of native APC devices by link DCE patch to fix wrong power and current values sent to DCO.

Try and report the result.

With respect.

(CID:138810578)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: โ€Ž2020-07-04 09:12 PM . Last Modified: โ€Ž2024-04-04 03:51 AM

In response to DCIM_Support
0 Likes
0
1726
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 09:12 PM . Last Modified: โ€Ž2024-04-04 03:51 AM

Good day


We have done the indicated test, the patch has been uploaded in DCE. In DCO, the external system integration was eliminated and added again, the devices were associated again and it does not yet report measured data of the rpdus.

I detail the activities that have been carried out after the migration to virtual machines:

The 3 DCE, DCO and Optimize virtual systems have been created, their corresponding backups have been restored.

In DCE, we have acquired the virtual license, its backup was restored and its license was added for 1000 nodes, the devices are detected correctly

In DCO, your backup was restored correctly, DCE and Optimize external systems integration was successfully completed. All the devices in each corresponding team were associated.

In Optimize, your backup was restored correctly.

The error it shows is: DCO is not capturing the measured data of the rpdus

These virtual servers are in test stage, so far we have detected this error of the non-reading of measured data of the rpdus, for that reason we can not put it into production.

(CID:138812398)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: โ€Ž2020-07-04 09:13 PM . Last Modified: โ€Ž2024-04-04 03:51 AM

In response to DCIM_Support
0 Likes
0
1726
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 09:13 PM . Last Modified: โ€Ž2024-04-04 03:51 AM

Dear Caroll Silva,

From your comments:

...The error it shows is: DCO is not capturing the measured data of the rpdus

In this case, this may be a DDF related problem. Please tell us which vendor with which rPDU models do you have this problem? Without this, it is impossible to solve your problem.

With respect.

(CID:138812706)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: โ€Ž2020-07-04 09:13 PM . Last Modified: โ€Ž2024-04-04 03:51 AM

In response to DCIM_Support
0 Likes
0
1726
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 09:13 PM . Last Modified: โ€Ž2024-04-04 03:51 AM

dear specialist

The PDUs are Liebert, but it seems that this is just one of the problems.

We still have the physical DCE, DCO and Optimize machines in production and, in this case, if they are registering some values; The rpdus measured data record solution file has already been  requested from the device area and they are working on it.

As for the virtual machines that have been created and are in the testing phase, I can send you some screens of the faults detected by mail and detail these problems in depth; we have used the support of our local area, but they indicate that in this way we could solve the problem soon

regards

(CID:139691905)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: โ€Ž2020-07-04 09:13 PM . Last Modified: โ€Ž2024-04-04 03:51 AM

In response to DCIM_Support
0 Likes
0
1726
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 09:13 PM . Last Modified: โ€Ž2024-04-04 03:51 AM

Dear Caroll Silva,

That is, as I expected, your problem is DDF related. You need to wait for an answer on your request from the DDF team.

With respect.

P.S.: I sent you my private e-mail.

(CID:139692217)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: โ€Ž2020-07-04 09:13 PM . Last Modified: โ€Ž2024-04-04 03:51 AM

In response to DCIM_Support
0 Likes
0
1726
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 09:13 PM . Last Modified: โ€Ž2024-04-04 03:51 AM

Dear Specialist

We have solved the issue of the visualization of the measured data in the DCO virtual machine.

We have updated DCO, to the latest version 8.2.12; we notice in the DCE monitoring that DCO displays an error message unknown status code for essential services.

What is missing from our configuration?

(CID:140216252)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: โ€Ž2020-07-04 09:13 PM . Last Modified: โ€Ž2024-04-04 03:50 AM

0 Likes
0
1726
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 09:13 PM . Last Modified: โ€Ž2024-04-04 03:50 AM

For DCO:

  1. Install DCO on the virtual server and restore a backup of the solution.
  2. Note you have to re-upload specific database drivers for ETL or custom developed transformations if you any of those.

Best,

Niels

 

(CID:133367539)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: โ€Ž2020-07-04 09:13 PM . Last Modified: โ€Ž2024-04-04 03:50 AM

0 Likes
0
1726
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 09:13 PM . Last Modified: โ€Ž2024-04-04 03:50 AM

Caroll. On the IT Optimize server. Which protocols is the customer using for server discovery?

If they are using the OS based protocols like WMI, VMware, SSH, and SNMP then I can provide instructions to backup the current ITO server and restore the backup on the newly installed ITO virtual machine.

If they are also using IPMI to discover management cards, then the process of backing up and restoring ITO is a little more involved.

Regards

Greg Sterling

(CID:133367569)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: โ€Ž2020-07-04 09:13 PM . Last Modified: โ€Ž2024-04-04 03:50 AM

0 Likes
0
1726
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 09:13 PM . Last Modified: โ€Ž2024-04-04 03:50 AM

Hello Greg

Usamos los protocolos VMware, SNMP, SSH, WMI en nuestro ITO, incluido IPMI

 

Regards

 

(CID:133373020)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: โ€Ž2020-07-04 09:13 PM . Last Modified: โ€Ž2023-10-22 03:02 AM

0 Likes
0
1726
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Subscribe to RSS Feed
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: โ€Ž2020-07-04 09:13 PM . Last Modified: โ€Ž2023-10-22 03:02 AM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of