Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

How to add Liebert / Emerson NXa UPS to DCE 7.2.0?

EcoStruxure IT forum

Schneider Electric support forum about installation and configuration for DCIM including EcoStruxure IT Expert, IT Advisor, Data Center Expert, and NetBotz

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure IT
  • EcoStruxure IT forum
  • How to add Liebert / Emerson NXa UPS to DCE 7.2.0?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Cory_McDonald
Admiral Cory_McDonald Admiral
124
Jef
Admiral Jef Admiral
110
gsterling
Captain gsterling Captain
71
APC_Steve
Captain APC_Steve Captain
65
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to EcoStruxure IT forum
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 01:51 PM . Last Modified: ‎2024-04-09 04:24 AM

0 Likes
4
741
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 01:51 PM . Last Modified: ‎2024-04-09 04:24 AM

How to add Liebert / Emerson NXa UPS to DCE 7.2.0?

We have DCE 7.2.0. I want to add Liebert /  Emerson NXa UPS to it. for which I allowed the IP of DCE in the UPS web console and run discovery. DCE discoved UPS as cooling unit and just shows its link status only. Please guide how can I monitor all the parameters of NXa UPS as we do of APC UPS systems.

Notice that I tried to update DDF through APC web site but the process failed.

(CID:99156460)

Labels
  • Labels:
  • Data Center Expert
Reply

Link copied. Please paste this link to share this article on your social media post.

  • All forum topics
  • Previous Topic
  • Next Topic
Replies 4
DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 01:51 PM . Last Modified: ‎2024-04-09 04:24 AM

0 Likes
0
742
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 01:51 PM . Last Modified: ‎2024-04-09 04:24 AM

Dear Syed,

You will need to add the Liebert/Emerson NXa UPS DDF file in order for DCE to discover the device via SNMP or Modbus Over TCP. 

Depending upon the type of the communication SNMP or Modbus Over TCP output from the UPS device, you need to fill in the DDF request form and send it to Multivendorsupport@apcc.com. 

Please email your DDF request to Multivendorsupport@apcc.com so that they will respond you with the DDF file. 

I hope this helps. 

Regards,

Bala

(CID:99156463)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 01:52 PM . Last Modified: ‎2024-04-09 04:24 AM

0 Likes
0
742
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 01:52 PM . Last Modified: ‎2024-04-09 04:24 AM

Hello Syed,

 

If you are on DCE 7.2.0 I would recommend upgrading to the newest version which is 7.2.7. If you only able to see the link status, it usually refers to a DDF problem. This version may not have the most up to date version of the Liebert DDF for your model. 

You can also email multivendorsupprt@apcc.com to acquire this DDF for your unit. Please send in the exact details of the Liebert unit, along with an SNMPWalk and the MIB file. They will be able to then send you the most recent DDF for this unit to import into the DCE client. 

 

Regards,

Breda

(CID:99156464)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 01:52 PM . Last Modified: ‎2024-04-09 04:24 AM

0 Likes
0
742
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 01:52 PM . Last Modified: ‎2024-04-09 04:24 AM

Hi Syed I had some Emerson DDF just in case you want to try them out...Rest you can try upgrading DCE to latest version and mail up multivendor support...

liebert.xml   liebert (1).xml

(CID:99156537)

Reply

Link copied. Please paste this link to share this article on your social media post.

DCIM_Support
Picard DCIM_Support
Picard

Posted: ‎2020-07-02 01:52 PM . Last Modified: ‎2023-10-31 11:03 PM

0 Likes
0
742
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

Posted: ‎2020-07-02 01:52 PM . Last Modified: ‎2023-10-31 11:03 PM

superhero.png

This question is closed for comments. You're welcome to start a new topic if you have further comments on this issue.

Reply

Link copied. Please paste this link to share this article on your social media post.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

https://idp-uat.se.com/authorize?client_id=llTc0ylhBFgpdEXCVkUDxpSio7Ckisb9&redirect_uri=https%3A%2F%2Fuat-community.se.com%2Fauth%2Foauth2callback&response_type=code&scope=openid+name+given_name+family_name+nickname+email+email_verified&referer=https%3A%2F%2Fcommunity.se.com%2Ft5%2FEcoStruxure-IT-forum%2FHow-to-add-Liebert-Emerson-NXa-UPS-to-DCE-7-2-0%2Ftd-p%2F204260%3Fsubscribe&screen_hint=signup
Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of